Radar Level Instrument

instrument radar isolation valve storage tanks

7 replies to this topic
Share this topic:
| More

#1 Lyne

Lyne

    Veteran Member

  • Members
  • 49 posts

Posted 24 August 2025 - 02:56 PM

Hello, please does a radar level instrument installed on a storage tank require an isolation valve ?

Edited by Lyne, 24 August 2025 - 02:57 PM.


#2 Pilesar

Pilesar

    Gold Member

  • Admin
  • 1,576 posts

Posted 24 August 2025 - 03:39 PM

I have seen many storage tanks open to the atmosphere without any isolation valves! Isolation valves might be required if the contents need to be isolated.



#3 breizh

breizh

    Gold Member

  • Admin
  • 6,802 posts

Posted 24 August 2025 - 06:11 PM

Hi.

No isolation valve. Check documentation from Vega or other vendors .

Breizh

Attached Files



#4 Lyne

Lyne

    Veteran Member

  • Members
  • 49 posts

Posted 24 August 2025 - 11:47 PM

Many thanks for your answers

#5 Lyne

Lyne

    Veteran Member

  • Members
  • 49 posts

Posted 24 August 2025 - 11:52 PM

I have seen many storage tanks open to the atmosphere without any isolation valves! Isolation valves might be required if the contents need to be isolated.



But if it’s a pressure transmitter it’s equipped with an isolation valve!

#6 breizh

breizh

    Gold Member

  • Admin
  • 6,802 posts

Posted 25 August 2025 - 03:32 AM

If your tank is breathing to atmosphere, there is no need for isolation valve.

Radar technology is reliable; isolation valve may be required for technology subject to maintenance. 

I've been using intensively this technology in chemical plants, on storage tanks reactors, buffer tanks, I don't remember Isolation valve installed.

Other reference E&H attached

Good luck.

Breizh

Attached Files



#7 Pilesar

Pilesar

    Gold Member

  • Admin
  • 1,576 posts

Posted 25 August 2025 - 07:21 AM

Can the level device be maintained safely while the storage tank is in service? If the storage tank contains lethal or highly hazardous substance, then I advise a block valve. Could you defend not having a block valve if the question were asked during a HAZOP study?



#8 Lyne

Lyne

    Veteran Member

  • Members
  • 49 posts

Posted 30 August 2025 - 01:01 AM

Can the level device be maintained safely while the storage tank is in service? If the storage tank contains lethal or highly hazardous substance, then I advise a block valve. Could you defend not having a block valve if the question were asked during a HAZOP study?



It’s an oil storage tank open to atmosphere,


thank you everyone