Thanks for sharing this. Discussing problems on a forum is very valuable and saves a lot of time. One person mentions something, another corrects or adds to it, and in this way the possible solution paths get narrower and sometimes someone provides the solution outright
Regarding the problem being discussed, yesterday I came across an article entitled “Reduce Pressure and Heat Losses Through Intelligent Utilisation of Pumps” (see Fig. 4), which presents the pressure profile of a system with a single pump at the source and distributed pumps in individual network sections. What doesn’t make sense to me is the return pressure profile. For water to always flow in the same direction, the pressure downstream of the valve (on the heat source side) must be lower than the pressure upstream of the valve (energy conservation principle).
I decided to check the pressure drop from the pump discharge to the most remote consumer - the supply pressure. I have several critical consumers, and I selected those with the lowest pressure difference across the heat exchanger. As expected, the pressure drops were positive, consistent with the pressure profile diagrams.
Then I checked the same for the return header. To my surprise, the pressure drops calculated from downstream of the valve at the heat exchanger to the pressure boosting station were both positive and negative. This is inconsistent with what is shown in the diagrams.
I concluded that the pressure downstream of the valve at the most remote consumer would be lower than the return pressure at the pressure boosting station in two cases.
The first case is when there is such a large heat deficit that everyone opens their valves downstream of the heat exchangers, causing the pressure in the pipeline to the end user to drop so much that the user receives no water at all - essentially trying to push water from an empty supply pipe into an empty return pipe.
The second case is when everything is operating correctly, meaning there is sufficient pressure at the supply side of the last consumer and the condition of more than 80 kPa is met, but that consumer’s valve is closed. Since it is the last one on the line, the water in the return pipeline drains, leaving the most remote section of the return line empty.
If the system actually behaves this way, then the control valve at the pressure boosting station should start closing when the pump is operating at maximum capacity and the pressure difference at the end consumer drops below 80 kPa. The effect of partially closing this valve in such a situation is to build up pressure upstream of the valve and restrict closer consumers, so that water can reach the most remote ones.
Just to be transparent - I also use AI to help translate my replies. I understand your posts without any problem, but I use a translator to make my own answers clearer and easier to follow 