I may not have described my thinking clearly enough. I’m not coming at this from a pump design background; I’m a software developer trying to understand the idea behind this type of control.
Let me try to explain how I currently understand the sequence of events, using a simple example.
Assume the pump can operate from 20–100% speed and is currently running at about 50%, slightly to the right of its best efficiency point. The differential pressure at the end users is controlled to a bit above 80 kPa.
When the weather gets colder, the customer valves open slightly, which increases the flow. As the flow increases, the control valve on the return side starts to close in order to prevent the pump from losing further differential pressure due to the higher flow.
At the same time, the higher flow through the network increases pressure losses in the pipes, and the available differential pressure at the most remote customers drops below 80 kPa. The VFD then increases pump speed, restoring the required differential pressure for those customers.
This topic interests me because I haven’t been able to get a clear explanation of this control concept from people I know on the process side. Recently I watched a “Process with Pat” video about designing pressure drops in piping systems, and it made me think about the return-pressure-based control. Since we effectively choose the pressure upstream of the control valve, it seems possible to define it as a function of flow (in practice it looks more like a band than a single curve, with a spread of around 100 kPa).
I’ve been going through some district heating literature and found piezometric diagrams (pressure profile) that explain how pressures are shaped in the network. What confused me is that older references usually assume constant flow networks, while in this case the flow varies significantly due to control on the customer side.