Hello everyone
I need your help about line sizing for PSV's, i'm sizing PSV's for a pipeline transporting a gas with the following data:
MW= 20.53 (mostly methane 71%)
Flowrate= 320 000 kg/hr
Density upstream = 184 kg/m3
Temperature= 100 °C
Pressure= 240 bar
Z factor = 0.89
Cp/Cv= 1.55
i used HYSYS safety analysis for sizing, i choosed blocked outlet scenario as the worst case scenario, so i discharged all the flowrate, HYSYS suggested 3 pilot PSV's, the simulation selected 2 J 3 (2500 x 300) for each PSV for a flowrate of 106 666 kg/hr, the problem i'm facing now is sizing the downstream lines, i took a mach number of 0.7, density of 2 kg/m3 at relieving.
hand calculation gave me a 10" pipe and the flare header around 20", these results seem weird to me, i would like to know if these are reasonable or my calculation are missing something.
thank you.