Hello everyone,
I want to know the back pressure incase of a relief through PSV in critical flow condition.
Case:
PSV set pressure is 84 Barg. and discharge in atm. flare header.
Flare Header Design pressure : 7 barg.
From these its obvious that the flow through the orifice will be chocked.
and mass flux will be limited to chocked flow. In such case what will happen to downstream pressure(backpressure).? pressure drop through PSV orifice will be 82-(~2)=80 bar or around 50% of upstream pressure(~42 bar), pressure drop required to attain chock flow)?
Can anybody guide?
|

Backpressure In Case Of Critical Flow Relief.
Started by Guest_Jaimin Patel_*, Aug 22 2007 12:25 AM
6 replies to this topic
Share this topic:
#1
Guest_Jaimin Patel_*
Posted 22 August 2007 - 12:25 AM
#2
Posted 22 August 2007 - 03:45 AM
Jaimin,
At choked flow condition, the flow passing through PSV will be more-or-less fix. Then the PSV downstream pressure will be the pressure drop (along the flare header) plus ATM.
HTH
JoeWong
At choked flow condition, the flow passing through PSV will be more-or-less fix. Then the PSV downstream pressure will be the pressure drop (along the flare header) plus ATM.
HTH
JoeWong
#3
Guest_Jaimin Patel_*
Posted 22 August 2007 - 06:34 AM
Does it mean that orifice of PRV will create pressure drop up to any limit ?
It doesnt limited by critical pressure ratio. It wil be the pressure diff between upstream pre. and downstream pressure generated by downstream system.
It doesnt limited by critical pressure ratio. It wil be the pressure diff between upstream pre. and downstream pressure generated by downstream system.
#4
Posted 22 August 2007 - 07:18 AM
The pressure at the outlet plane of the nozzle (not orifice) will be set by the pressure that gives sonic flow. Outside the nozzle there will be expanding jet(s) and shock wave(s). Across the shock there are step changes in pressure (loss) and entropy. The pressure downstream of the shock equals that stated by JoeWong, "the pressure drop (along the flare header) plus ATM." A shock wave is very, very thin and this irreversible pressure loss happens extremely fast. I recommend reading Shapiro's The Dynamics and Thermodynamics of Compressible Fluid Flow.
#5
Posted 22 August 2007 - 09:30 AM
I'm going to see if I can simplfy this a bit. You determined your worst case scenario, therefore you mave your maximum required relieving rate. Assumning we are discussing 100% gas/vapor flow, you apply the API equation to calculate the required PSV orifice you need. When you applied this equation, you are assuming a back pressure effect, even if it is zero. You then use a "1" as the back pressure correction factor in the API equation.
You choose a PSV. Now, you obtain the certified (stamped or rated) capacity of this PSV and use this flow in your calculation to determine PSV tail pipe and header size or pressure drop if the size if fixed. You can start at the flare and work backwards. The pressure at the flare (or whatever is your final destination) should be fixed and we'll say atmospheric. As the gas/vapor flows from the PSV outlet to the flare, pressure builds up in the piping, this is commonly called the built-up backpressure. The final pressure drop in the piping determined by fluid flow equations will give you a backpressure at the PSV outlet flange. You then check this against the charts to see if the backpressure is too high such that you either have too small of a tail pipe or you adjust the PSV size by using a backpressure correction factor of something less than one (the charts will give this to you) in the API equation. This could cause the required PSV size to go up in size.
PSV sizing can be trial-and-error if the tail pipe and header system is too small.
You choose a PSV. Now, you obtain the certified (stamped or rated) capacity of this PSV and use this flow in your calculation to determine PSV tail pipe and header size or pressure drop if the size if fixed. You can start at the flare and work backwards. The pressure at the flare (or whatever is your final destination) should be fixed and we'll say atmospheric. As the gas/vapor flows from the PSV outlet to the flare, pressure builds up in the piping, this is commonly called the built-up backpressure. The final pressure drop in the piping determined by fluid flow equations will give you a backpressure at the PSV outlet flange. You then check this against the charts to see if the backpressure is too high such that you either have too small of a tail pipe or you adjust the PSV size by using a backpressure correction factor of something less than one (the charts will give this to you) in the API equation. This could cause the required PSV size to go up in size.
PSV sizing can be trial-and-error if the tail pipe and header system is too small.
#6
Guest_Jaimin Patel_*
Posted 23 August 2007 - 07:15 PM
Dear latexman/pleckner/JoeWong
Thanks for explanation.
Its clear that up to critical pressure ratio pressure drop is created by orifice. After that shock wave creates the pressure drop and keep downstream pressure equals to pressure drop in the discharge piping plus atm pressure.
What should be the design pressure of discharge tail pipe and flare header?
1) For tail pipe it should be based on discharge pressure calculated using critical pressure ratio.
2) For header it should be based on max pre due to pressure drop plus atm. pressure considering simultaneous release from more than one valve.
Is this correct ?
Thanks for explanation.
Its clear that up to critical pressure ratio pressure drop is created by orifice. After that shock wave creates the pressure drop and keep downstream pressure equals to pressure drop in the discharge piping plus atm pressure.
What should be the design pressure of discharge tail pipe and flare header?
1) For tail pipe it should be based on discharge pressure calculated using critical pressure ratio.
2) For header it should be based on max pre due to pressure drop plus atm. pressure considering simultaneous release from more than one valve.
Is this correct ?
#7
Posted 24 August 2007 - 05:39 AM
There is a discontinuity between the PSV throat and the PSV outlet flange. You must break your analysis up into two parts, the first being what happens in the PSV and the second what happens in the downstream piping. The cirtical pressure ratio you keep referring to is that in the PSV, not in the piping.
Again, you calculate the pressure drop in the piping downstream from the PSV, usually backwards starting at the destination point where you know the final pressure, and determine the backpressure at the PSV flange. Again, this has nothing to do with the critical pressure ratio you are referring to. Once you have this value, you can set your piping design pressure. (Note that you can go forwards also but then this will have to be a trial-and-error calculation. Going backwards may be able to eliminate the trial-and-error.)
In general, if this is a balanced bellows PSV then the maximum backpressure should be something less than or equal to around 50% of the PSV set pressure. You can then add whatever safety factor you normally use (I use 10% or 25 psi, whichever is greater, above the maximum operating pressure) to set a design pressure.
If this is an open system, my design pressure will typically be the same all the way from start to end using the highest pressure I calculate.
Again, you calculate the pressure drop in the piping downstream from the PSV, usually backwards starting at the destination point where you know the final pressure, and determine the backpressure at the PSV flange. Again, this has nothing to do with the critical pressure ratio you are referring to. Once you have this value, you can set your piping design pressure. (Note that you can go forwards also but then this will have to be a trial-and-error calculation. Going backwards may be able to eliminate the trial-and-error.)
In general, if this is a balanced bellows PSV then the maximum backpressure should be something less than or equal to around 50% of the PSV set pressure. You can then add whatever safety factor you normally use (I use 10% or 25 psi, whichever is greater, above the maximum operating pressure) to set a design pressure.
If this is an open system, my design pressure will typically be the same all the way from start to end using the highest pressure I calculate.
Similar Topics
Critical Pressure For Choke Valve SizingStarted by Guest_Sherif Morsi_* , 07 Nov 2017 |
|
![]() |
||
Heat Exchanger Steam FlowStarted by Guest_aliebrahem17_* , 25 Nov 2024 |
|
![]() |
||
![]() Flow Through Normally No Flow LineStarted by Guest_iippure_* , 08 Apr 2025 |
|
![]() |
||
![]() Flare Header Reverse FlowStarted by Guest_Ahmadhamzahperta_* , 04 Apr 2025 |
|
![]() |
||
![]() Dynamic Simulation After Feed Flow ReductionStarted by Guest_Kakashi-01_* , 20 Mar 2025 |
|
![]() |