Posted 08 October 2007 - 06:25 AM
In response to your last post:
1. My original statement is correct. The set pressure for this secondary PSV protecting against a fire can be as high as 10% over MAWP. The allowable overpressure/accumulation will still be 21% over MAWP.
In addition, if I were to be protecting a vessel from any scenario, other than fire, with more than one PSV, then those PSVs also do not have to have equal set pressures. The allowable overpressure/accumulation in this case is 16% over MAWP.
2. I also said that the liquid relieving scenario would have to be credible. If it is not a credible relieving scenario then you would not need to calculate the PSV size based on a liquid relief.
What makes the scenario credible in many instances is you, the Process Engineer. Have you designed the vessel for pump shut-off? Have you taken into account that the pump is not centrifugal but a positive displacement pump? How about if I am tranfering liquid using pressurized gas?
I would indeed try to design out the scenario. Sometimes it is only a matter of cost. Making equipment inherently safe is always the way to go. Relying on a relief device should be your last resort.
And as I said before, with some very special exceptions, EVERY ASME coded vessel must be provided with some type of pressure relief device. If you can't find a credible scenario, we usually just use thermal expansion as our scenario and install a minimal 1/2" x 1" or 3/4" x 1" PSV (depending on the manufacturer and model) and move on to other things.
3. If I have one PSV protecting the column, condenser and reflux drum and the PSV is on the reflux drum (many feet away from the column) what will the pressure be in the column during relief? The pressure at the PSV is essentially set pressure + allowable overpressure. What does that make the pressure at the column?
API wants you to put the PSV as close to the source of overpressure as possible, not many feet away. If you have to put the PSV many feet away, drop the set pressure so the pressure in the column won't exceed its allowable maximum during relief. Another solution would be putting a PSV on the column, as we've been mentioning, so it is closer to the source of overpressure. And again, if we have some isoation between at least one of the equipment pieces we've been discussing here a second PSV is going to be needed.
If you are going to get involved in relief systems then you need the proper reference library:
1. API RP520, 7th Edition, January 2000
2. API Standard 521
3. ASME Section VIII, Div 1 (or your location's pertinent Codes)
4. "Guidelines for Pressure Relief and Effluent Handling Systems", Center for Chemical Process Safety (CCPS) for the American Institute of Chemical Engineers (AIChE), (1998) New York
5. Fisher, H. G., Forrest, H. S., Grossel, S. S., Huff, J. E., Muller, A. R., Noronha, J. A., Shaw, D. A., and Tilley, B. J. (1992). "Emergency Relief System Design Using DIERS Technology: The DIERS Project Manual. AIChE, New York.
6. Fauske, H. K. "Revisitng DIERS Two-Phase Methodology for Reactive Systems Twenty Years later", Process Safety Progress, (AIChE; Vol. 25, No. 3), September 2006
7. "Easily Size Relief Devices and Piping for Two-Phase Flow", J. Leung, CEP, December 1996
8. Darby, R., Self, F. E., and Edwards, V. H. "Properly Size Pressure-Relief Valves for Two-Phase flow", Chemical Engineering Magazine, June 2002
9. Darby, R. "Size Safety-Relief Valves for Any Conditions", Chemical Engineering Magazine, September 2005
10. Simpson, L. L. "Estimate Two-Phase Flow in Safety Devices", Chemical Engineering Magazine, August 1991
11. Ouderkirk, R. "Rigorously Size Relief Valves for Supercritical Fluids", CEP, August 2002
12. Leckner, P. Six Part Series on Rupture Disks, Chemical Engineers' Resource Page
Various Websites including:
(1) The Chemical Engineers' Resource Page Forum on Pressure Relief Devices
(2) www.fauske.com
Is this extensive? You bet it is! Will you have time to read and understand all of this? NO WAY!!!! I've been doing this stuff for 20 years and still haven't gotten it all down. But I consider these to be MUST HAVES in any library if you are indeed serious about pressure relief system design. If you only are doing this occasionally, then References 1 thru 3 will be good enough as long as there is someone around that has the rest and is over-seeing your work.