i want to know if the flow coefficient Cv has a relation with the response time of the valve.
because i can't make my choice between the volume booster and the quick exhaust vale. this in the target to improve the response time in both the opening and closing of the valve
|

Control Valve
Started by medbg, Nov 07 2007 04:34 PM
3 replies to this topic
Share this topic:
#1
Posted 07 November 2007 - 04:34 PM
#2
Posted 07 November 2007 - 05:57 PM
medbg:
I've had to get involved with response times for control valves - especially Shutdown Valves (SDVs) and Blowdown valves (BDVs) - when developing P&IDs and Hazop action items.
The CV, in my opinion, has no bearing on the response time. I have never found it to be a factor. The response time has, in my cases, always relied on the type and make of actuator employed on the subject SDV or BDV. The speed of the controller signal and its strength also have had a bearing - but I've never had to worry about the inherent CV on the control valve, as long as I selected the correct size of valve. Granted, the larger the valve (& the CV), the more difficult it is to make a control valve operate rapidly. Perhaps I am wrong, but that has been my experience to date.
#3
Posted 08 November 2007 - 08:40 PM
Mr. Montemayor,
Please allow me to drop my supplementary comments...
medbg,
If the control valve associate with a ON-OFF control function e.g. in some drum handling low liquid loading with intermittent peak, response time may be required to minimize spurious HIGH-HIGH level trip.
Another occasion where response time may be associated with the opening of control valve is the compressor anti-surge control valve.
Above examples only relate the response time for full close to full open BUT still no relation between CV and response time.
JoeWong
Please allow me to drop my supplementary comments...
medbg,
If the control valve associate with a ON-OFF control function e.g. in some drum handling low liquid loading with intermittent peak, response time may be required to minimize spurious HIGH-HIGH level trip.
Another occasion where response time may be associated with the opening of control valve is the compressor anti-surge control valve.
Above examples only relate the response time for full close to full open BUT still no relation between CV and response time.
JoeWong

#4
Posted 25 November 2007 - 11:09 AM
Dear,
Addition to the comments by the Mr. Montemayer and Mr Joe,
Here is one link where we will find how to calculate the responce time of the control valve,
http://www.rosscontrols.com/vresp.htm
Addition to the comments by the Mr. Montemayer and Mr Joe,
Here is one link where we will find how to calculate the responce time of the control valve,
http://www.rosscontrols.com/vresp.htm
Similar Topics
Critical Pressure For Choke Valve SizingStarted by Guest_Sherif Morsi_* , 07 Nov 2017 |
|
![]() |
||
Check Valve FailureStarted by Guest_Falah_* , 26 Mar 2025 |
|
![]() |
||
Multiport Selector Valve (Msv)Started by Guest__1angelia23_* , 12 Mar 2025 |
|
![]() |
||
![]() Valve Cavity - Pressure Relief ValveStarted by Guest_CS10_* , 20 Feb 2025 |
|
![]() |
||
![]() Valve Cv InputsStarted by Guest_QuantumEng_* , 01 Apr 2024 |
|
![]() |