Dear JoeWong,
One new correction in 2007 edition is that API limit the depressuring rules to
carbon steel vessels and I do not know about the reason and also what about the other vessels?
This criterion is based on the vessel-wall temperature versus stress to rupture and applies generally to
carbon steel vessels with a wall thickness of approximately 25,4 mm (1 in) or more. "
QUOTE
shall keep in mind that the 1" criteria is only applicable to Pool-fire.
And even in this new edition they do not speak explicitly about the depressuring time for vessels with thickness less than 25 mm!
"Vessels with thinner walls generally require a somewhat faster depressuring rate. The required depressuring rate depends on the metallurgy of the vessel, the thickness and initial temperature of the vessel wall and the rate of heat input."
Technip company criteria for concerned vessels:
For wall thickness smaller than 25 mm, following rule shall be applied:
- Wall thickness < 25 mm : 15 minutes minus 3 minutes for each 5 mm decrease in thickness
Total company criteria for depressuring time:
"As a general rule, time to achieve the final pressure level after an EDP has been initiated (1)
shall be, by default:
· 15 minutes for piping and vessels containing hydrocarbon, both gas or liquid
· 8 minutes for vessels containing LPG's or light condensate to avoid the risk of BLEVE.
Note 1: These requirements are applicable only to emergency depressurisation and are not
valid for depressurisation imposed by process reasons
If these criteria were to lead to unacceptably large hydrocarbon disposal devices (either flare or
cold vent) then the two following exceptions could be envisaged:
· Depressuring time for capacities with a wall thickness larger than 25 mm could be
enlarged on the basis of 3 more minutes for every 5 mm in excess of 25 mm and with an
absolute maximum of 30 minutes. This approach is allowed only if one vessel is
concerned (or one group of vessels with similar characteristics served by a common BDV)
and if it is demonstrated that nozzles, instrument tappings and other possible spots where
metal thickness is less than 25 mm do not represent a weak point, likely to leak before full
depressurisation is achieved.
· Credit can be taken for passive fire protection when provided. In this case the time to
achieve full depressurisation shall be as per requirements above, lengthened by the time
it takes for the vessel (or piping) wall to reach its critical temperature (generally 400°C)
and considering the characteristics of the fire to which it will be submitted.
Sizing of BDV's to match the above criteria shall be based on the assumption that during a fire,
all streams incoming and outgoing the system are shutdown'd and all internal heat sources
within the process, if any, have ceased."