Thanks a lot for your valuable comments and clarification.
The MP steam header is designed for 12 barg.
QUOTE
Per ASME B31.3, you may exceed design pressure based on frequency of events and duration but must never exceed test pressure. ASME B31.3 does not specifically talk about scenarios so I would fall on both ASME Section VIII, Div 1 and API Std 521. In this system it appears you may be able to exceed the test pressure of the MP steam pipe if there were a tube rupture so in this system I would say you need a PSV on the MP steam line to limit this pressure excursion.
Sorry, but I misunderstood your mean! You supplied additional information to support this idea that tube side can exeed its design pressure(depend on frequency and duration) and consequently need not to be provided with a psv but after that you proposed to use a psv to protect the tube side against tube rupture scenario!

As a rough estimation the tube side test pressure can be 150% of its design pressure(12 barg) which equals a value of 18 barg.The shell side operating pressure is 20 barg.If tube rupture occures the tube side will expose to a pressure higher than its test pressure and so should be provided with a protective relieving device.It's OK?