A) Several times I have seen centrifugal pumps protected by pressure transmitter mounted on suction side. The idea of these instruments is to indicate no flow conditions sensing pressure. But that works? The alarm set is usually atmospheric pressure (when liquid level is loss) but…..
1) What happen when I have vacuum at the pump suction under normal operation? It seems that this kind of protection is useless.
2) What happen if, by mistake, an operator close pump suction valve? The centrifugal pump makes low pressure or vacuum enough to be detected by the transmitter?
Based on this I prefer Flow Switch for pump protection.

For example, think about a tank and pump system working under two different condition. . At LLL operation condition the pump is taking water from a tank when the level is 2 meters, the discharge pressure is (let say) 2 Kg/cm2g. Follow this we would set the alarm to stop the pump at 2.5 Kg/cm2g (0.5 Kg/cm2g more than the normal pressure: shut off pressure).
But, at HLL operation condition the pump is taking water from a tank when the level is 8 meters, the discharge pump pressure will be 2.6 Kg/cm2g (increased by the head of water) and, under the previous scheme’s of pump protections, the pump would stop immediately.
Based on this I think that mounting pressure transmitter on the discharge doesn’t work for small pump. You need a good difference between normal operation point pressure and shut off pressure. So for this case a prefer Flow Switch for pump protection.
About points A and B. What do you think? Do you agree? I am missing something. I would appreciate very much your opinion.
Thanks
Ariel