There is a temperature control loop across a cooler as attached. (I appreciate Art’s EXCEL file which help me to finish the attached draft quickly.)
The hot fluid A at 150C is cooled by a cooler. There is a bypass control valve helping to maintain the target temperature at 50C, particularly in winter. I believe this loop will function well if the fluid is passing continuously.
However, the ZCV valve will open (once per 10 hours) and close (10 hours after being opened), then wait for another 10hours to open again. To my understanding, the temperature control loop won’t achieve steady target temperature (50C) in the first certain minutes when ZCV is open after 10 hours waiting if the loop is set on AUTO mode control.
The TIC indication will be first much higher than 50C (TV may be fully open during waiting period), even may be closed to source temperature 150C and then lower than 50C, finally will reach 50C after cycles of fluctuation. This is not appropriate in terms of process and valve maintenance requirement, particularly for large size valves.
So, if my understanding is correct, manually operating the TV in the first several minutes may be better to get stable target temperature. But the designer wants to keep auto control.
To avoid the valve shaking severely or temperature fluctuation, is there a better control strategy to automatically maintain steady temperature (say 50C) at TIC during all the time for this kind of intermittent operation?
Thanks.