Hi all,
FYI i am learning hysys. I am trying to simulate flash drum with control over feed flow, vapor flow rate and liquid flow rate. I added all controllers. But to my surprise when i change set point, actually valve is closing completely. Please help in this regard.
And, also how to tune the controller according to the requirement?
|
|
Problem Regarding Hysys
Started by Mystified, Nov 09 2008 02:15 AM
3 replies to this topic
Share this topic:
#1
Posted 09 November 2008 - 02:15 AM
#2
Posted 15 November 2008 - 01:18 PM
Raaj,
It's difficult to give any comment - there is no flowsheet available, control logic setup, independent and dependent variables etc. Almost nothing, in one word.
It's difficult to give any comment - there is no flowsheet available, control logic setup, independent and dependent variables etc. Almost nothing, in one word.
#3
Posted 16 November 2008 - 10:50 AM
Dear,
Zauberberg is right come up with the flowsheet of the flash drum with schematic of the configured control system. So that it would be easy to comment.
Zauberberg is right come up with the flowsheet of the flash drum with schematic of the configured control system. So that it would be easy to comment.
#4
Posted 17 November 2008 - 10:22 AM
QUOTE (RAAJ @ Nov 9 2008, 07:15 AM) <{POST_SNAPBACK}>
Hi all,
FYI i am learning hysys. I am trying to simulate flash drum with control over feed flow, vapor flow rate and liquid flow rate. I added all controllers. But to my surprise when i change set point, actually valve is closing completely. Please help in this regard.
And, also how to tune the controller according to the requirement?
FYI i am learning hysys. I am trying to simulate flash drum with control over feed flow, vapor flow rate and liquid flow rate. I added all controllers. But to my surprise when i change set point, actually valve is closing completely. Please help in this regard.
And, also how to tune the controller according to the requirement?
Sounds to me like one of two things. Either
(1) You've got your controller acting in "direct" rather than "reverse".
You need to tell the controller that if the measured variable (flow) is too low, it needs to increase the controller output (which should be connected to the valve position). Or...
(2) Your valve is set to be fail open. This causes the valve to say "if I get no signal from the controller, I should drive myself 100% open". This then means that when the controller increases its signal (i.e. moving away from 0 signal), the valve closes in on itself.
See if either of those help.
- Steve.
Similar Topics
Importing Component Stream Data From Hysys To Excel Using VbaStarted by Guest_TimL_* , 17 Aug 2018 |
|
|
||
Sulfuric Acid Plant Aspen Hysys HelpStarted by Guest_kazuki222_* , 29 Apr 2026 |
|
|
||
Hysys Separator Carryover Setup And Phase EnvelopeStarted by Guest_powerox29_* , 05 Jan 2026 |
|
|
||
Beginner Question: Inlet Separator Design In Aspen Hysys (Natural Gas,Started by Guest_NewEng2030_* , 12 Feb 2026 |
|
|
||
Use Of Case Studt On Aspen Hysys SimulationStarted by Guest_vtf1221_* , 13 Dec 2025 |
|
|

FB