Posted 29 April 2009 - 06:18 AM
I think that what he is asking is whether or not he should consider any vapor generation from vessel "A" during an external fire in the fire zone around "A" as a cause for overpressure in vessel "B".
My thought would be that no, if vessel "A" has a properly sized PSV to handle the vapor generated during a fire around "A," you would not consider the excess generation from the 121% (121 psi in this case) when sizing a PSV for "B." HOWEVER, I would say that you DO need to consider the vapor generated in Vessel "A" that would cause vessel "B" to exceed its MAWP-i.e., the vapor flow from "A" that would be in excess of the vessel "B" MAWP (84 psi) but less than the pressure at which the vessel "A" PSV begins to lift (100 psi). It may make it easier if you want to consider setting the vessel "A" PSV for 84 psi...just food for thought. I would also note that this scenario would not be an external fire around vessel "B", and thus would be a 10% overpressure process related upset rather than a 21% overpressure external fire scenario.