What is the pressure drop criteria for sizing control valves which is in a system almost wholly governed by static pressure. The dynamic losses are very small compared to the static pressure drop.
|
|
Control Valve Sizing
Started by ayan_dg, Apr 24 2009 09:28 PM
7 replies to this topic
Share this topic:
#1
Posted 24 April 2009 - 09:28 PM
#2
Posted 25 April 2009 - 12:46 AM
ayan_dg
I undersand from Luyben that pressure drop across a valve should be about 20-30% of the total pressure drop in the line. I don't know how good is that, but it might be a good starting point.
I undersand from Luyben that pressure drop across a valve should be about 20-30% of the total pressure drop in the line. I don't know how good is that, but it might be a good starting point.
#3
Posted 25 April 2009 - 02:05 AM
QUOTE (ayan_dg @ Apr 25 2009, 10:28 AM) <{POST_SNAPBACK}>
What is the pressure drop criteria for sizing control valves which is in a system almost wholly governed by static pressure. The dynamic losses are very small compared to the static pressure drop.
Ayan ,
Let you try to download from Internet Valves mnaufacturer handbook s, you will get the right answer .
I would suggest Masoneilan or Fisher. Probably somewhere between 0.5 and 1.5 bars
Regards
Breizh
#4
Posted 25 April 2009 - 09:01 AM
QUOTE (ayan_dg @ Apr 24 2009, 10:28 PM) <{POST_SNAPBACK}>
What is the pressure drop criteria for sizing control valves which is in a system almost wholly governed by static pressure. The dynamic losses are very small compared to the static pressure drop.
Ayan_dg,
Please check out the following links. One is from our good old cheresources.
http://www.cheresour...m/valvezz.shtml
http://www.sbt.sieme...on/15370186.pdf
http://www.incyam.co...nload/dl_51.pdf
The above mentioned links provide a good insight about control valves and also have specific sections dealing with pressure drops.
Regards,
Ankur.
#5
Posted 27 April 2009 - 08:43 AM
Dear,
If the dynamic losses are small, than use 10 psig as a minimum for the control valve pressure drop.
If the dynamic losses are high, than the delta P across the control valve is 25 % of the dynamic losses.
This criteria is used by many reputed EPC companies like Bechtel and SNC lavalin E&C.
Hope this helps.
ARAZA
If the dynamic losses are small, than use 10 psig as a minimum for the control valve pressure drop.
If the dynamic losses are high, than the delta P across the control valve is 25 % of the dynamic losses.
This criteria is used by many reputed EPC companies like Bechtel and SNC lavalin E&C.
Hope this helps.
ARAZA
QUOTE (ayan_dg @ Apr 24 2009, 10:28 PM) <{POST_SNAPBACK}>
What is the pressure drop criteria for sizing control valves which is in a system almost wholly governed by static pressure. The dynamic losses are very small compared to the static pressure drop.
#6
Posted 30 April 2009 - 12:36 AM
QUOTE (ayan_dg @ Apr 24 2009, 10:28 PM) <{POST_SNAPBACK}>
What is the pressure drop criteria for sizing control valves which is in a system almost wholly governed by static pressure. The dynamic losses are very small compared to the static pressure drop.
Dear Ayan
We do not need any criteria under such situation. The pressure drop for sizing is determined by the differential static pressure between upstream and downstream.
regards
S.AHMAd
#7
Posted 30 April 2009 - 01:18 AM
Dear S.Ahmad,
this is OK if the source and destination pressure are fixed, so obviously you cannot do anything. But say you can increase the source pressure; so, for better control what is the pressure drop?
#8
Posted 30 April 2009 - 11:24 AM
QUOTE (ayan_dg @ Apr 29 2009, 10:18 PM) <{POST_SNAPBACK}>
But say you can increase the source pressure; so, for better control what is the pressure drop?
You might use control of the source pressure as a means of controlling your flowrate, if that is what you desire to control - you didn't tell us. With no controls, your flowrate would be such that the pressure + static head of the source vessel = the pressure + static head of the destination vessel - frictional losses. Add a control valve and the concept remains the same; you just add the control valve dP to the frictional losses. If frictional losses are truly negligable, the the CV pressure drop is just the difference between the two vessels' static + superimposed pressures.
Similar Topics
Steam Drum SizingStarted by Guest_nastaran_* , 01 Dec 2025 |
|
|
||
Help Needed –Valve Causing High Pressure In Downstream VesselStarted by Guest_Alaa55_* , 27 Nov 2025 |
|
|
||
Thermal Relief Valve For A Fire CaseStarted by Guest_QuantumEng_* , 19 Nov 2025 |
|
|
||
Equal Load Sharing And Anti-Surge ControlStarted by Guest_panoska_* , 02 Nov 2025 |
|
|
||
Control Strategy For 2 Air Compressors In ParallelStarted by Guest_panoska_* , 31 Oct 2025 |
|
|

FB