Nitrogen Purging Of Pipeline
Started by jescabrera, May 29 2009 01:12 PM
8 replies to this topic
Share this topic:
#1
Posted 29 May 2009 - 01:12 PM
I'm looking for a procedure for the nitrogen purging of pipelines after hydrostatic testing. Please advise.
#2
Posted 29 May 2009 - 01:25 PM
Could you give us more detail please.
#3
Posted 30 May 2009 - 06:03 AM
Direct-buried chilled water and steam/condensate piping that will be installed but will not be in service for some time. We'd like to dry the inside of the piping after hydrostatic testing and then "pickle" the piping until the system is placed in service.
#4
Posted 30 May 2009 - 07:32 AM
Well the foremost issue that I find is how will you know that the line has been properly dried? Is the line very long? Being buried that would make it more difficult, especially considering that there might be low spots that accumulated moisture.
The purge would be simple. Inject at one end through a flowmeter to see the flow rate.
In tank work there are various methods to determine how much purge is needed to purge.T y this reference:
Purge reference
Otherwise you might search further.
The purge would be simple. Inject at one end through a flowmeter to see the flow rate.
In tank work there are various methods to determine how much purge is needed to purge.T y this reference:
Purge reference
Otherwise you might search further.
#5
Posted 30 May 2009 - 07:35 AM
I am not sure that the hyper link is working. It seems that the link is dead. Since this was posted originally for open use on the internet, and I made a copy of it, I am attaching the file.
Attached Files
#6
Posted 01 June 2009 - 02:15 AM
QUOTE (proinwv @ May 30 2009, 08:32 AM) <{POST_SNAPBACK}>
The purge would be simple. Inject at one end through a flowmeter to see the flow rate.
Would you please explain above in detail?
#7
Posted 01 June 2009 - 05:13 AM
Thanks for the information but could you please provide more information? For example, are there any parameters such as the temperature of the nitrogen that needs to be injected, the flowrate, the types of fittings to use, etc.
#8
Posted 01 June 2009 - 06:01 AM
Please excuse the bluntness, but if you are asking these questions one would question whether you should be taking on this project.
I suggest that you consult with some experienced engineer(s) in your organization, or engage the services of a consultant.
I suggest that you consult with some experienced engineer(s) in your organization, or engage the services of a consultant.
#9
Posted 13 November 2011 - 05:51 AM
thanks
thanks dear i got it
I am not sure that the hyper link is working. It seems that the link is dead. Since this was posted originally for open use on the internet, and I made a copy of it, I am attaching the file.
thanks dear i got it
Similar Topics
Nitrogen Capacity Tankfarm During WinterStarted by Guest_jango_* , 03 Feb 2025 |
|
![]() |
||
Determining Pipeline Design PressureStarted by Guest_applepe_* , 05 Dec 2024 |
|
![]() |
||
Purging Blowdown SystemStarted by Guest_Ade24_* , 29 Nov 2024 |
|
![]() |
||
![]() ![]() Energy Saving In Pump By Reducing Pressure Drop In Downstream PipelineStarted by Guest_Srinivas Agastheeswaran_* , 19 Nov 2024 |
|
![]() |
||
![]() Nitrogen Leak Test On PipeStarted by Guest_mesbah_* , 24 Oct 2024 |
|
![]() |