I am currently evaluating some existing steam PRVs which are vented to the atmosphere via an open pipe. One puzzling fact I noticed after I did some calculations to the tail pipe is that these outlet pipings of steam PRVs (which are vented to the atmosphere) will achieve Mach No. more than 1 (i.e. supersonic) when I use the PRV's RATED capacity and the existing open pipe diameter.
My question is: Is it theoretically possible for the PRV's outlet piping to reach more than mach no 1 during relieving?
Or
will the outlet pipe get choked at mach no.1, hence restricting the actual relieving capacity of the PRV?
The open pipe connected to the PRV outlet is about 7 meters long.
Meanwhile, I tried searching around books to find out more on compressible flow behaviour, and I found one interesting explanation from C&R Chem. Eng. Vol. 1, Chapter 4, Section 4.5:
"Unlike the orifice or nozzle, the pipeline maintains the area of flow constant and equal
to its cross-sectional area. There is no possibility therefore of the gas expanding laterally.
Supersonic flow conditions can be reached in pipeline installations in a manner similar
to that encountered in flow through a nozzle, but not within the pipe itself unless the
gas enters the pipe at a supersonic velocity."
From the above paragraph, I am interpreting that it is possible for PRV discharge outlet to achieve supersonic flow condition (Mach > 1) because sonic flow conditions are created through the PRV's orifice. Whereas if a compressible fluid started off as a sub-sonic flow in a pipe, it will never be able to reach supersonic flow conditions no matter how much dP is provided along the pipe, as it will get choked at sonic condition (M = 1).
Greatly appreciate replies and comments to my question/ interpretation.