This post is about the use of SIS in the place of PSV in a low pressure storage tank. The systen consists of a 3-phase separator that receives oil from well. The produced water is sent to low pressure storage tanks that operate around 100 mbar g. While evaluating the over pressure scenario for the tanks, gas blowby from the separator to the tank was identified as a cause for overpressure, but was ruled out saying that there is a SIL3 protection for low level shut down in the tank.In addition there is also a high pressure shutdown in the tank inlet.
My concerns are,
1. The low level shut down in the separator and the high pressure shut down in the tank are not 2 independent layers, as the logic solver for both the loop is the same ESD system.
2.Also an ESD system is not a HIPS system (triple redundant). Please correct me if i am wrong.
3.According to API 521. each vessel/equipment should be self protected mechanically. But SIS can be used as an alternative like in the case of HIPPS.
4.But according to API 14C,
Refer to API RP 14C including sections 4.2.1.4, A.4.2.2.2, A.4.3.2 and the associated tables listed.
A low level signal can interlock a shutdown valve on the liquid outlet (or inlet) as the primary protection from gas blowby. Safety devices downstream provide secondary protection for the downstream equipment.
This is a totally opposite of API 521, or thats what i understand.May be I am wrong.
I really appreciate the valuable input from the forum members.
I hve attached a rough sketch of the system with the protections.
Many Thanks in advance