Technically, this makes sense but I'd never realized that it was explicitly allowed according to API standards. Primarily, i think this has application in justifying existing installations that exceed the 10% limit, but are sized for a fire scenario. It would also apply to process upset cases in which the PSV is set below the MAWP.
I don't recall ever hearing or reading any discussion on this topic. Is this widely practiced? It hasn't been practiced in my company but I think it should be. Do any of you have any comments on this? Thanks.
Here's the whole text of this section:
3.3.3.1.3 In a conventional pressure relief valve application, built-up back pressure should not exceed 10% of the set pressure at 10% allowable overpressure. A higher maximum allowable built-up back pressure may be used for allowable overpressures greater than 10% provided the built-up back pressure does not exceed the allowable overpressure. When the superimposed back pressure is constant, the spring load may be reduced to compensate for the superimposed back pressure. In this case, it is recommended that the built-up back pressure should not exceed the allowable overpressure. When the downstream piping is designed within the above back pressure criteria, no back pressure capacity correction(Kb = 1.0) is required in the valve sizing equations, for gases at critical flow or for liquids. When the back pressure is expected to exceed these specified limits, a balanced or pilotoperated pressure relief valve should be specified.