After replacement of steam traps I have to estimate the steam savings obtained. the traps replaced are 1/2 " thermodynamic type traps which were passing heavily(blowing steam). the service is tracing steam & inlet P=4 Kg/cm2 @148 DEG C & outlet connected to atmospheric pressure Steam condensate tank(with arrangement to condense the generated flash steam. Can somebody suggest a formula or thumb rule? Thanks in Advance...
|

Estimating Steam Loss
Started by ASH25320, Dec 09 2009 11:01 AM
2 replies to this topic
Share this topic:
#1
Posted 09 December 2009 - 11:01 AM
#2
Posted 09 December 2009 - 03:31 PM
There are two factors that effect amount of steam through a blowing trap.
The choking effect of steam flowing through a small orifice
The amount of condensate present. Condensate will flash and further choke the flow and, if you have condensate flowing through the trap you don't have loss of steam!
The only real way to measure this is in a calorimeter, which you can't in the real world conditions.
SO....
I have seen using a conservative estimate of 10% of the rated full capacity of the steam trap at your differential pressure conditions. Sounds low but if you add it up over a 24/7/365 period it is a LOT of steam.
The choking effect of steam flowing through a small orifice
The amount of condensate present. Condensate will flash and further choke the flow and, if you have condensate flowing through the trap you don't have loss of steam!
The only real way to measure this is in a calorimeter, which you can't in the real world conditions.
SO....
I have seen using a conservative estimate of 10% of the rated full capacity of the steam trap at your differential pressure conditions. Sounds low but if you add it up over a 24/7/365 period it is a LOT of steam.
#3
Posted 11 December 2009 - 03:34 PM
In addition to guide rule by joesteam, I have to point out that steam loss through a trap depends much on the trap situation, even though operators try to minimize steam loss (if possible by "setting" the trap). That is why some people support that electrical tracing can be cheaper than steam tracing, since steam losses can be 3 times the actual steam needed!
If you know the steam consumed now and that consumed before (under almost same weather and fluid conditions), you can find the steam saving by difference. Steam can be measured by installing an orifice, but you should have measured its flow rate before.
If you know the steam consumed now and that consumed before (under almost same weather and fluid conditions), you can find the steam saving by difference. Steam can be measured by installing an orifice, but you should have measured its flow rate before.
Similar Topics
Steam Pressure In Heat ExchangerStarted by Guest_mvanrijnbach_* , 15 Apr 2025 |
|
![]() |
||
Heat Exchanger Steam FlowStarted by Guest_aliebrahem17_* , 25 Nov 2024 |
|
![]() |
||
![]() Steam Carrying Liquid From The Sour Water Stripping TowerStarted by Guest_kaidlut_* , 12 Sep 2024 |
|
![]() |
||
Converting Superheated Steam To Saturated SteamStarted by Guest_addiesalsabil_* , 10 Sep 2023 |
|
![]() |
||
Steam BlowingStarted by Guest_the_avinche2309_* , 24 Feb 2025 |
|
![]() |