The datasheets of PCV says:
Inlet = 400KPag
Outlet = 380KPag
IA Failure = retain last state.
RO datasheet:
Max flow = 22kg/hr
Max. Delta = 380 KPag
So the sequence of process is:
400KPag purge gas (Natural gas) to PCV
I can see that RO is here to control purge gas flow so that if PCV malfunctions. But the DP against RO is so high... wasn't it enough to have a RO alone on this line who could drop the pressure from 400KPag to 2KPag (it is already dropping 380KPag to 2KPag).
Is there any other purpose of having PCV + RO control on purge gas that I'm not able to grasp??