Dear ALL,
Anyone know how to make a hand calculation of radiation level?
Or any reference to make it?
Normally to calculate this we use such a software like PHAST or CFD.
regards
demank
Hand Calculation Of Radiation Level
Started by demank, Feb 15 2010 01:55 AM
Posted 15 February 2010 - 01:55 AM
Posted 15 February 2010 - 05:51 AM
Based on API Standard 521 (5th edition) section 6.4.2.3.3:
If you assume the flame to have a single radiant epicentre:
K = tau*F*Q/(4*pi*D^2)
with:
K = the radiant heat intensity at the object being considered in kW/m2
tau = the fraction of the radiated heat transmitted through atmosphere (use tau = 1 as a conservative approach)
F = the fraction of heat radiated (see table 10 in API std 521, values depend on flame size and fuel type and can range from ~0.1 to ~0.3)
Q = the heat release (based on Lower Heating Value), in kW
D = distance from the epicentre of the flame to the object being considered, in m
You can calculate Q based on fuel flowrate and LHV. For F you can use 0.3 as a conservative value. With values F=0.3 and tau = 1, the formula simplifies to:
K = 0.024*Q/D^2
with:
K = 0.024*Q/D^2