Shailu,
What a coincidence this is? Just a week back I was studying a proposal for a Jet A-1 fuel storage terminal and I had some reference documents (Jet A-1 tank datasheets) to refer to for the various appurtenances mentioned in that document for Jet A-1 storage tanks. Although some of the data provided was questionable.
The auto bleeder (bleeder vent) on the floating roof and rim vent are clearly required as per the guidelines of API 650 for closed floating roof tanks as mentioned by Fallah. The question is whether your tanks is designed according to API 650.
Now the question comes to the requirment of a process vent and its location. Without doubt a process vent is required. Again as far as the location of this process vent, it should be provided on the fixed roof of the tank and not on the floating roof since the auto bleeder on the floating roof takes care of any venting requirement between the extremely small vapor space and the floating roof. This process vent could be either an open vent or in the form of a PVRV.
Also do not forget to provide an emergency vent or blow-off hatch on the fixed roof for external fire case scenario.
An additional point that was discussed during the proposal study I was doing related to requirement of nitrogen blanketing of the space between the fixed roof and the floating for the Jet A-1 tanks. After due discussion it was concluded that nitrogen blanketing was not required. The following logic was provided for not providing any nitrogen blanketing:
1. Nitrogen blanketing in petroleum product tanks is provided to prevent a flammable mixture being formed with air which could cause a fire and / or explosion if the concentration of the hydrocarbon and air mixture falls between its LFL & UFL.
2. Because there is a floating roof with rim sealing along the periphery of the closed floating roof tanks, the leakage from the rim seal to the vapor space between the floating roof and the fixed roof is negligible. Thus the vapor space between the floating roof and the fixed roof has very little hydrocarbon vapor and more of air. The mixture is therefore very lean or in other words it is below the LFL of the hydrocarbon-air mixture and thus precludes the danger of a fire or explosion.
3. The extremely small vapor space between the floating roof and the liquid level has mostly hydrocarbon vapors and since the rim seal of the floating roof prevents any large scale ingress of air from the vapor space between the floating roof and the fixed roof to the small vapor space between the liquid level and floating roof, the vapors in the small vapor space are hydrocarbon rich vapors or in other words above the UFL of the air-hydrocarbon mixture thereby precluding any flammable or explosive environment.
The above arguments provide a basis for not having any nitrogen blanketing in petroleum product being stored in a closed floating roof tank.
For those young chemical engineers who have little idea of how a closed floating roof tank looks like the attached sectional drawing of a closed floating roof tank should provide a good pictorial representation.