Hello,
This topic has perhaps been discussed many times and I have found some useful guidance here:
http://www.aft.com/d...low-Reprint.pdf
I would greatly appreciate some discussion to help me to better understand how to deal with choked flow in pressure drop / line sizing calculations.
Background:
I am sizing a blow-down line on a natural gas pipeline for maintenance blow-down of pipework and equipment. I have sized a restriction orifice plate in order to give me a suitable time to achieve depressurization but also to limit the extent of the zone required for hazardous area classification so that the zone does not extend beyond the boundary fence for abnormal operation of the valve.
The system will normally be used for blow-down of a fixed volume during maintenance routines, but there is always a possibility that the vent is unlocked and used abnormally, so I am basing my calculations on the peak flows at maximum system operating pressure.
There are a number of other vents, process vents and relief valve vents and I am intending to tie-in all of the laterals from each source into a common vent header with release to atmosphere.
Problem 1:
Focussing for now just on the high pressure maintenance vent lateral design:
I initially I performed my blowdown calculations by treating the system as a simple orifice, but now I need to size the lateral and determine maximum system pressures in the lateral to specify design pressures. I will be installing a flame arrestor downstream of the orifice and so need to provide operating pressures and design conditions.
The process conditions are as follows:
Fluid: natural gas (Mw = 18.5)
Z = 0.92 at upstream condition
Maximum upstream system pressure: 33.8 bara
Upstream temperature: 10ºC. Joule thomson effect ignored for initial assessment
Orifice size: 6mm NB
Vent lateral size: Initially guessed to be 1" NB, but 2" NB likely to be selected to prevent additonal choking in the lateral piping
Common vent header size 4" NB
Common vent header disposes to atmospherice pressure
For the orifice calculation, I determined that the flow is choked and therefore the downstream pressure from the orifice must be equal to the critical pressure, which I calculated to be 18.45 bara. For the given upstream pressure the maximum choked flow through the orifice is ~500 kg/hr.
I have built a compressible flow pressure drop spreadsheet (that I have divided into many segments to create a network for all fittings, area changes and junctions etc). Mach no. is calculated for the inlet and outlet of each segment to determine where the choke points will occur.
Method 1: If I work through the pressure drop calculation with upstream pressure (downstream of orifice) set at 18.45 bara the resulting outlet pressure (release to atmosphere) will not be atmospheric (for 1" or 2" pipe sizing).
For this calculation the flow was based on the maximum orifice choked flow.
Method 2: If I work backwards ie from the vent outlet at atmospheric pressure, using the maximum orifice flow again, I can calculate the upstream pressure (downstream of the orifice) and this is significantly lower that the critical pressure, approx 3.5 bara for a 1" pipe and 1.2 bara for a 2" pipe.
Question 1: which method is correct to determine the operating pressure for the flame arrestor?
Discussion:
The reference document (link at top) states:
'the pressure drop across the shock wave in choked flow cannot be calculated directly. The only recourse is to use the choked flowrate as a new boundary condition on the pipe downstream of the shock wave.'
I have used the choked flow as the boundary condition (or limiting mass flow into the vent lateral), but I am still struggling with how to deal with the pressure discontinuity.
Question 2: f I was to determine the maximum operating pressure in the vent pipework downstream to determine a suitable design condition, do I state that the maximum operating pressure in the vent is equal to 18.45 bara or equal to 3.5 bara (or 1.2 bara if 2" lateral used)?
Problem 2:
As previously mentioned the HP vent lateral will tie-in to a common header. If I size the lateral in 1" NB further choking will occur at the reducing T-piece adjoining header. By installing 2" I can avoid this.
For my own interest I would like to understand the implications (for if I assumed the vent lateral is 1") and again understand how I deal with the pressure discontinuity that will occur at the reducing T-piece junction with the common 4" header.
Question 3: Does the shock wave caused by choking dissipate instantly at the junction or could this continue downstream for a given (unknown at this stage) distance and affect the back-pressure in the common header?
Again, if I calculate back-wards from the vent outlet to atmosphere, the calculated back-pressure at the junction is significantly lower and does not cause too much back-pressure to the relief valves connected to the system.
Any advise or discussion would be greatly appreciated.
Kind Regards,
Ian