Fallah:
Thank you for following up with a logical concern about the proper and correct way to size the required inert gas requirement flow rate to a storage tank while it is subjected to pump-out as well as in-breathing. I concur with your comments and am in agreement with your statement that the inert gas flow rate required may be more related to the inbreathing instead of pump-out in the case of very large tanks.
You will note that I stated that in the past – in certain applications – I have found the opposite effect to be true. In my specific cases, I recall that I was dealing with tanks in the capacities of 3,000 barrels and less. This topic now brings to the forefront the definition of what constitutes a “large” storage tank. I would consider a tank of 100,000 barrels as a large storage tank (134 ft diam. x 40 ft high); however, some experts have indicated that they consider this as a “small” tank. So I am always inclined to define the tank size.
I recall when discussing this topic with my design group that it was decided that the scenario was that it was the coldest day in 50 years and that the pump-out rate was approximately 150 – 200 gpm, with a wind speed of 25 mph. Under these given conditions there would be no agitation or turbulence in the tank’s vapor space and therefore, the convection currents in the vapor space were practically nil while the incoming inert gas was much hotter (25 oC) than the outside ambient temperature. Therefore, it was concluded that the heat transfer rate between the tank’s wall and the inert gas blanket was expected to be very weak, with a negligible vapor volume decrease (and corresponding pressure decrease) due to temperature reduction. This left the pump-out rate as being the main cause for a pressure decrease in the vapor space – during the pump-out time which was (as I recall) approximately 1.5 hours. Considering that the time involved was relatively short, it was decided that the temperature effect on the tank’s vapor volume would be negligible during that period.
However, if the tank involved is a much larger one – over 100,000 barrels – and the wind speeds are increased at a very cold temperature, then I think it is conceivable that the effect of inbreathing may be predominant in this type of application – especially if the pump-out time is prolonged. In any event each application should be calculated, checked, and carefully discussed in cases where a hazardous situation can arise.
Your thoughts and comments would be appreciated in view of the importance of this topic with regards to safety.