Steam Jacketing For Natural Gas Line
Posted 04 October 2014 - 12:58 AM
Subject:
I have to design steam jacketing system for natural gas piping to rise natural temperature from 10 Deg.C to 45 Deg.C in one of our project.
Technical Parameters:
Following are the natural gas & LP steam parameters
Cold Fluid:
Natural Gas flow – 45612 kg/hr
Inlet Gas Pressure – 45 kg/cm2(g)
Inlet Gas Temperature – 10 Deg.C
Outlet Gas temperature – 45 Deg.C
Hot Fluid:
Inlet Steam Pressure – 6.0 - 6.5 Kg/cm2(g)
Inlet Steam Temperature – 190 Deg.C
Outlet condition – Condensate
Concerns/Problems:
Here is the following concern where in i am looking for your valuable suggestion.
1. Inside Heat transfer coefficient as per my calculation (Natural gas side) is ~ 1500 Kcal/Hr/m2/k. I am doubting that this is on higher side for gases(may be due to first of its kind for me), hence i request you all experties to suggest the optimum inside heat transfer coefficient which usually consider for these type of applications.
Arrived calculation result is based on following parameters
Nu = 0.023 * (Red)^4/5 * (Pr)^0.4
Reynolds No. (Red) = r*V*D/u
r - Density of natural gas @ 45 Kg/cm2(g)
u - Dynamic viscosity - 0.00002 N-s/m2
Diameter of pipe(D) = 260.3 mm
Prandtl no.(Pr) = u*Cp/k
k - 0.03 w/m/k @ 25 Deg.C
Cp - 0.5 Kcal/kg/k
Inside heat transfer coefficient(Hi) = Nu*k/D
I am seeking your valuable opinion/suggestion to design this.
Your quick response is highly appreciable
Rgds
krishna
Posted 04 October 2014 - 01:28 AM
krishna,
Value of overall HTC in your case (Heater with Steam-Gas fluids) should be in the range of 30-300 W/m2-K (26-260 kcal/h/m2/°C). Refer the links below:
http://www.engineeri...l/transfer.html
http://blackmonk.co....r-coefficients/
Posted 04 October 2014 - 02:23 AM
Thank you very much Mr. Ankur for your reply,
I have gone through your links where in values given typically for heat exchanger, where as my requirement is pipe jacketing(I.e inner pipe - natural gas & Outer Pipe - Steam), hence can we use same values as mentioned in heat exchangers (i.e Steam to Gas)
Rgds
krishna
Posted 04 October 2014 - 02:56 AM
Krishna,
Yes, with the value to be considered on the lower side of the range given due to less flow turbulence in the pipe-in-pipe type of heat exchanger.
Posted 04 October 2014 - 03:42 AM
Posted 04 October 2014 - 06:21 AM
You would need to post your calculation if you want to know where you went wrong.
Maybe it is simply because you seem to work with a mix of metric and SI units.
When I do a calculation for inside inside heat transfer coefficient hi using your data and method, I find
hi = ~ 500 W/m2.K = ~ 430 kcal/h.m2.K
Combined with condensing steam this would give an overall heat transfer coefficient U = ~ 350 W/m2.K = ~ 300 kcal/h.m2.K
That U value is at the upper end of the range of the typical U's published in various books and websites, but if I would have used more realistic values for natural gas physical properties the calculated hi and U would have been even higher.
Duty = ~ 1100 kW (based on Cp = 2.5 kJ/kg.K) and LMTD = ~ 135 oC so you can estimate required A and L. Make sure you add plenty of overdesign.
Edited by PingPong, 04 October 2014 - 06:31 AM.
Maximum Natural Gas Flow Through OrificeStarted by Guest_ukrche_* , Today, 08:23 AM |
Control Philosophy In Steam ReboilersStarted by Guest_halkeshhulk_* , 07 May 2024 |
Heating Of Natural GasStarted by Guest_kaidlut_* , 01 May 2024 |
Tank Blanketing With Natural Gas/ Vapor Recovery SystemStarted by Guest_MethanolPlant_* , 26 Apr 2024 |
Flash Steam Vessel SizingStarted by Guest_JohnFields343_* , 24 Apr 2024 |