Relief Scenario For Sizing A Psv

psv fire case blocked in thermal expansion

This topic has been archived. This means that you cannot reply to this topic.
6 replies to this topic
Share this topic:
| More

#1 S Manikandan

S Manikandan

    Brand New Member

  • Members
  • 6 posts

Posted 10 January 2015 - 03:09 AM

Good morning all,

 

I have a doubt in selection of scenarios for sizing PSV.

 

There is diesel storage system, which consists of a diesel storage tank, diesel pump and fuelling system. The diesel pumps transfer diesel from storage tank to fuelling station. Two diesel distribution filters (1W+1S) with a PSV in each filter, are placed at the pump discharge line. Please refer attached process flow diagram.

 

For sizing  PSV in the filter, Do I need to consider blocked in thermal expansion case or fire case? or both?

 

 

Please clarify my doubt.

 

Thanks in advance

 

Regards

S Manikandan

Attached Files



#2 fallah

fallah

    Gold Member

  • ChE Plus Subscriber
  • 4,954 posts

Posted 10 January 2015 - 03:52 AM

Hi,

 

At first please specify pump discharge pressure corresponding to the pump minimum flow in blocked discharge conditions. Also specify the design pressure of the filters.



#3 Fakhri

Fakhri

    Junior Member

  • Members
  • 14 posts

Posted 10 January 2015 - 07:42 AM

Hi Manikandan,

In my opinion, you only need to consider the thermal expansion case due to shut-in conditions. The fire case is not valid scenario since the flash point of diesel is higher than the ambient temperature. This will not be able to form flamable vapour if it is released

 

Rgds,

 

 

Fakhri



#4 S Manikandan

S Manikandan

    Brand New Member

  • Members
  • 6 posts

Posted 12 January 2015 - 03:04 AM

Dear Mr.Fallah,

 

The discharge pressure of the pump corresponding to the Min. flow is 6 barg

and design pressure of the filters is 10 barg, which is equal to the PSV set pressure.

 

Thanks and Regards

S Manikandan



#5 fallah

fallah

    Gold Member

  • ChE Plus Subscriber
  • 4,954 posts

Posted 12 January 2015 - 03:27 AM

Dear S.Manikandan,

 

Then the blocked outlet case can't be a credible scenario for mentioned PSVs. The only credible scenario can over pressure the filters more than 10 barg would be fire case provided that the filters are located in a fire zone and lower than the height of 7.6 m from grade ... 


Edited by fallah, 12 January 2015 - 03:33 AM.


#6 S Manikandan

S Manikandan

    Brand New Member

  • Members
  • 6 posts

Posted 18 January 2015 - 11:41 PM

Thanks to Mr.Fallah and Mr.Fakhri for your replies.

 

 Thanks and Regards

S Manikandan



#7 Hamid_r_2003

Hamid_r_2003

    Junior Member

  • Members
  • 13 posts

Posted 06 February 2015 - 06:44 PM

as far as I know for such system which is full of liquid you just need a TSV for thermal expansion.