Inlet Nozzle Connection For Tank
#1
Posted 05 September 2010 - 12:45 PM
Assume Some general atmoshperic Tank!
I have an inlet line to this tank. This inlet line can be be connected to the Bottom of the tank.
Also this connection can be connected to the top section.
For top section we may need a dip pipe to the bottom section to aviod electrostatic issue.
Also for bottom connection we need a Check valve to avoid back flow.
Is there any general practice for this issue?
When top or when bottom?
General Case: Atmoshperic Tank, With or without blanketing, hydrocarbon or water
Ghasem Bashiri
#2
Posted 07 September 2010 - 12:26 PM
Exceptions to this practice have been seen for specific reasons, such as below.
1. Tank close to sea, danger of fuel into the sea in case of valve leakage.
2. Fuel tank loaded by truck.
3. Rather small tanks feeded directly from production units (phosphoric or sulfuric acid), mainly when roof of tanks do not exceed the piperack level.
4. Tanks fed by gravity flow (not always the case in gravity flow).
5. When tanks are also used for thickenning (e.g. for phosphoric acid thickeners).
Splash filling is not recommended in these "exceptions" (except 5).
Probably the rule can be: think of a low nozzle at first, then see whether there is some reason to change opinion (such as mentioned, or other).
#3
Posted 07 September 2010 - 12:53 PM
To my knowledge concerning refineries, liquid tanks have their nozzles at the low area of their cylindrical surface (close to bottom) according to API 650. And as close to the ground as possible (distance specified by tank wall strength of material), to facilitate emptying.
Post originator asked for location of inlet nozzle but seems your response not refered to it.
Anyway,IMO emptying would be done by the outlet line through outlet nozzle and usually in the case of the inlet nozzle at near the bottom,a check valve should be installed before inlet connection to avoid emptying by reverse flow through inlet line.
Edited by fallah, 07 September 2010 - 12:56 PM.
#4
Posted 08 September 2010 - 02:57 AM
When connecting to the bottom the following should be considered:
1. The position of the inlet line must be higher than the position of the outlet line of the tank as well as the water line if the tank will be used to store crude oil.
2. Check valve in addition to either a ball or a gate valve must be installed on the line to prevent backflow.
3. The inlet nozzle must be at least one pipe side lower than the outlet line.
When connecting to the top the following should be considered:
1. The position of the inlet must be lower than the design liquid level and higher than the position of LSH/LSHH
2. There must be adequate pressure to take it to the top of the tank other wise there will be no flow.
3. The line into the tank should be lowered to the bottom.
I hope this will be of help to you.
Regards
Ochuko.
Edited by Art Montemayor, 08 September 2010 - 10:59 AM.
#5
Posted 08 September 2010 - 02:12 PM
All nozzles to transfer liquid (either in or out) are usually located close to bottom. Said "exceptions" refer to liquid inlet nozzles. Let it be an additional clarification to the stand posted by kkala of Sep 7th.Post originator asked for location of inlet nozzle but seems your response not referred to it.
#6
Posted 08 September 2010 - 02:50 PM
#7
Posted 09 September 2010 - 09:15 AM
As a general note, there are often good reasons for deviating from "normal" practices, and the reasons for doing so are not always obvious. My best rule fo thumb to all, coming from someone who is frequently critical of rules of thumb, is to first do no harm. Often that means to not change things (as in from a previous design) if you don't have a good reason for doing so. Especially if the previous design is up and successfully running.
#8
Posted 13 September 2010 - 04:28 PM
1. A diagram of LNG terminal (ship unloading) indicates all lines feed LNG tanks from their top, using either a splashplate or standpipe pipe inside tanks. LNG out comes also from top, through submergible pumps (acting as booster pumps).
2. On the contrary lines in and out for LPG (and similar liquefied gases) in spheres are connected to the lowest part of them (sometimes on a manhole cover), apparently for convenience (short feed line, easiness to empty).
3. It is not recommended to connect water lines close to bottom of hydrocarbon tanks. Backflow will sometime occur, even if two check valves are placed in series, so water side will get contaminated with oil. That is especially true when water is discharged automatically, so that the isolation valve close to tank remains open .
Above refinery practice is applied even for oily water (they do not want more oily in it) and can be generalized to any liquid not accepting any contamination from the stored one.
Similar Topics
![]() Phosphoric Acid 56% Tank LiningStarted by Guest_Phosphoric123_* , 20 Apr 2025 |
|
![]() |
||
![]() Tank Inlet Diffuser LengthStarted by Guest_RAFAELDAVE_0752_* , 08 Apr 2025 |
|
![]() |
||
Inlet Line Not Free DrainingStarted by Guest_Asifdcet_* , 07 Apr 2025 |
|
![]() |
||
Discussion - Predict Storage Tank Heat Transfer Precisely By Jimmy D KStarted by Guest_raj shekhar_* , 25 Mar 2025 |
|
![]() |
||
Tank Filing TimeStarted by Guest_not_mikhail_* , 17 Mar 2025 |
|
![]() |