I am a very junior (just graduated) process engineer in the oil and gas industry.
Please see attached drawing. I have been asked to examine whether a relief valve on a 3-phase separator V-100, which has been sized for overpressure from blanket gas, needs to be sized for liquid relief as well.
Using API 520 Section 5.8 (Sizing for Liquid Relief: PRVs Requiring Capacity Certification), I have sized the RV and obtained a larger required area than for the gas relief case (~300 mm2 vs. ~100 mm2). I did this using the approach whereby the Produced Water is entering the vessel at its maximum flow rate, and all the vessel outlets are closed.
My question is:
Is this scenario too conservative? Is it double jeopardy to assume that the vessel high high level trip has failed and all outlets are blocked? (I talked to someone who said it is feasible that during startup someone could have left the outlets closed and started to fill the vessel.)
Just to reiterate, referring to the attached drawing, the RV-100A has currently been sized for gas relief, for a fail open of PCV-100A with PCV-100B remaining closed. What I have done is size it for a fail open of FCV-050A (maximum liquid pump-in rate), with all outlets blocked. I want to know the correct approach to sizing RV-100A.
Attached Files
Edited by Mark E. Smith, 21 December 2010 - 11:56 PM.