Flare Radiation
#1
Posted 12 May 2011 - 05:27 AM
Maximum allowable personnel exposure time to particular heat radiation level proposed in API RP 521 .
for personal continuous exposure Heat radiation at any location shall be limited to 1.58 kW/m2.
my question:
Is like this limitation also for equipment installation?
It was requested to install one hydrocarbon condensate storage tank in the area which impacted by flare radiation.
Introducing useful document are highly appreciated.
#2
Posted 13 June 2011 - 09:13 AM
Additional safety criterion for a liquid hydrocarbon storage tank (assumed to be a drum, ie a pressure vessel) exposed to radiation (from flare + sun simultaneously) can be as follows:
The vessel should have a PRV directed to flare header and covering the fire case. If heat input due to fire per API RP 520 is higher than heat input due to radiation, the vessel fire protection will cover the case of incident radiation letting some vapor go through the PRV. This is expected to be the valid case in the plurality of cases; fire can be close to drum, while flare gases are burnt at a height. In case that incident radiation is higher than fire heat input, PRV has to be sized accordingly.
In case of max 1.58 kW/m2 at ground level (value rather small, compare to max solar radiation = 1 kW/m2) no tank shelter to protect workers near the drum from flare radiation seems necessary.
#3
Posted 16 June 2011 - 02:56 AM
volvo parts
#4
Posted 16 June 2011 - 01:59 PM
Would have been more helpful to know if you are designing or constructing around that area. Usually up to 1500 btu/h/ft2 (please convert to SI) is permitted in design but if your personnel are uncomfortable then put a shield and work. Though the deisgn says 1,500 btu/h/ft2 normally there is only purge gas through the flare and its not hot around that place to work. You have about 10 to 20 minutes for escape if soemthing blows out and the flare goes boom !
Maditha
#5
Posted 19 June 2011 - 12:50 AM
Attached Files
#6
Posted 20 June 2011 - 11:26 AM
API 2218 for fireproofing practices in its appendix C, section C.3 has following on radiation flux for equipments:
"Q: What is the allowable heat flux exposure for equipment?
A: While no single number can be used for all equipment, one company uses a value of 300°C (572°F) as a safe operating maximum for steel structures and process equipment. They then calculate acceptable radiation guidelines. Computer modeling equates 300°C to an exposure of approximately 12.5 kW/m2 (4000 BTU/hr-ft2) for exposure without fireproofing or water spray; for vulnerable structures they lower this to as little as 8 kW/m2 (2500 BTU/hr-ft2). They require fireproofing for any case where the fire scenario envisions direct fire impingement."
Shell DEP 80.45.10.10, section 6.3.2 suggests 6.3 kW/m2 radiation flux for equipments in flare within sterile area.
This radiation flux criteria can be used to decide surface temperature of equipment. Design temperature of equipment should be more than calculated surface temperature.
Irrespective of radiation flux, it is this surface temperature that would decide flare stack height (in addition to other criteria like flux for human exposure, dispersion of combustion products etc).
Regards,
Sachin
#7
Posted 21 June 2011 - 01:24 PM
Dear All:
Maximum allowable personnel exposure time to particular heat radiation level proposed in API RP 521 .
for personal continuous exposure Heat radiation at any location shall be limited to 1.58 kW/m2.
my question:
Is like this limitation also for equipment installation?
It was requested to install one hydrocarbon condensate storage tank in the area which impacted by flare radiation.
Introducing useful document are highly appreciated.
You need to calculate the Stack hight and Mditha already give you clue, 'ie' 1500BTU/hr/Ft2 , Henceforth you can estimate the limitation for equipment installation.
Toor
Similar Topics
![]() Flare Header Reverse FlowStarted by Guest_Ahmadhamzahperta_* , 04 Apr 2025 |
|
![]() |
||
Psv On Ko Drum With Flame Arrestor At Flare Vent LineStarted by Guest_Tintin2024_* , 29 Oct 2024 |
|
![]() |
||
Slope Of Flare Sub Headers / Tail Pipes And Main HeadersStarted by Guest_Sawsan_* , 02 Dec 2024 |
|
![]() |
||
![]() Flare And Venting SystemStarted by Guest_miz19_* , 10 Jul 2024 |
|
![]() |
||
Handling The Limited Capacity Of Flare SystemStarted by Guest__1angelia23_* , 05 Apr 2024 |
|
![]() |