Storage Tank Design
Started by benoyjohn, Mar 11 2003 12:16 AM
2 replies to this topic
Share this topic:
#1
Posted 11 March 2003 - 12:16 AM
I have a few querries.
* What is the max vacuum for which API 620 tanks can be designed? Can
tanks be designed for vacuum higher than 45 mm WC? Which code shoud be
reffered to?
* What is the size limitation of storage tanks designed with frangible
roofs API 650 ?
* Where are slope in tank bottoms used? Where are slope out tank
bottoms used?
Regards
Benoy John
Process Engineer
Bechtel Ltd,
New Delhi.
* What is the max vacuum for which API 620 tanks can be designed? Can
tanks be designed for vacuum higher than 45 mm WC? Which code shoud be
reffered to?
* What is the size limitation of storage tanks designed with frangible
roofs API 650 ?
* Where are slope in tank bottoms used? Where are slope out tank
bottoms used?
Regards
Benoy John
Process Engineer
Bechtel Ltd,
New Delhi.
#2
Posted 11 April 2003 - 01:34 PM
With regard to your tank questions:
1) API-620, like API-650, require vacuum protection devices for protection against collapse.
If a new tank is being specified, the design vacuum pressure noted on the datasheets should be about -5 to -10 inches WC ( enough to actuate the vacuum protection device)
2) I understand that only "small tanks" can use fragible roofs. This issue is being evaluated by an API-650 code group. Installing a pressure relief device on "small diameter" tanks is the only realistic way to provide some protection.
3) Sloped bottoms on large tanks are discussed in a book titled "Aboveground Storage tanks" by Phillip Myers. Essentially, "cone-up" designs are the only ones in use. "Cone-down tanks corrode in a place tht is difficult to repair. These sloped bottomed tanks have been used in crude oil storage.( the slope was necessary to promote water drainage)
However, I believe that the trend is to now use flat bottomed tanks with superior internal coatings
Just my thoughts/recollections.................
MJC
1) API-620, like API-650, require vacuum protection devices for protection against collapse.
If a new tank is being specified, the design vacuum pressure noted on the datasheets should be about -5 to -10 inches WC ( enough to actuate the vacuum protection device)
2) I understand that only "small tanks" can use fragible roofs. This issue is being evaluated by an API-650 code group. Installing a pressure relief device on "small diameter" tanks is the only realistic way to provide some protection.
3) Sloped bottoms on large tanks are discussed in a book titled "Aboveground Storage tanks" by Phillip Myers. Essentially, "cone-up" designs are the only ones in use. "Cone-down tanks corrode in a place tht is difficult to repair. These sloped bottomed tanks have been used in crude oil storage.( the slope was necessary to promote water drainage)
However, I believe that the trend is to now use flat bottomed tanks with superior internal coatings
Just my thoughts/recollections.................
MJC
#3
Posted 19 April 2012 - 04:11 PM
3) Sloped bottoms on large tanks are discussed in a book titled "Aboveground Storage tanks" by Phillip Myers. Essentially, "cone-up" designs are the only ones in use. "Cone-down tanks corrode in a place tht is difficult to repair. These sloped bottomed tanks have been used in crude oil storage.( the slope was necessary to promote water drainage)
Just my thoughts/recollections.................
MJC
Dear Experts,
Is anybody has this book or know where I can find it? I really need this book now. Appriciate if can help me in this regards.
Afshin
Edited by Afshin, 19 April 2012 - 04:12 PM.
Similar Topics
![]() Steam Sparger In Atmospheric Water TankStarted by Guest_owe_* , 16 May 2025 |
|
![]() |
||
![]() Scrubber DesignStarted by Guest_nasss_* , 07 Aug 2024 |
|
![]() |
||
Refinery Lpg Deethanizer Column DesignStarted by Guest_Ilyes_* , 15 Feb 2025 |
|
![]() |
||
![]() Phosphoric Acid 56% Tank LiningStarted by Guest_Phosphoric123_* , 20 Apr 2025 |
|
![]() |
||
![]() Tank Inlet Diffuser LengthStarted by Guest_RAFAELDAVE_0752_* , 08 Apr 2025 |
|
![]() |