Following view represents my understanding. Comments would be welcomed to correct the picture.
1. Purpose of PCV is to keep constant pressure upstream of TCV to "facilitate" TCV function. Actually the TCV reduces pressure of downstream steam, thus lowering its temperature and resulting heat transfer rate (see "steam control" option at
http://www.driedger...._sh/CE4_SH.html).
2. In this sense PCV had better be removed, if one of the two valves should be to avoid unstable control. See example of "steam control" above, where there is only one control valve at ingoing steam (the valve in condensate pot merely controls condensate exit).
But probability of unstable control because of two valves seems quite remote in the specific case. Fluid is compressible. Response of PCV is quite fast, as concluded from steam headers pressure control; TCV must be slower, taking input from liquid temperature at a different stream. See also
http://www.cheresour...alve-in-series/.
Nevertheless flow stability criteria on a line with two control valves in series may exist, advice on this matter would be appreciated. It might involve elements from control theory not so familiar to Chemical Engineers. Concerning an LPG vaporizer (1984), Instrument Dept placed PCV and TCV on ingoing steam, assuring of no problem. Process was reluctant to accept two on line control valves, then project stopped without result.
3. Concerning such control, I have not seen PCV alone, either, probably too "nervous" for the service.
4. If it were existing status, I would leave working system as is. But it seems to be a new design.
Edited by kkala, 22 November 2011 - 12:19 PM.