How To Improve The Condenser / Heat Exchanger Performance
#1
Posted 22 August 2012 - 08:58 AM
Any body guide / suggest me to improve the performance / efficiency of condenser / heat exchanger for pharmaceutical industry applications. Please help me in check list / parameters to be monitored while distillation of methanol under atmospherically..
#2
Posted 25 August 2012 - 11:16 AM
Will you please give your present conditions?
- Present shell and tube heat exchanger configuration;
- Coolant flow and temperatures;
- methanol vapor flow.
SRShah
#3
Posted 25 August 2012 - 09:13 PM
A sketch or simple PId as mass and heat balances (as suggested) will help to support your query ! Please let us know your problem .
Breizh
#4
Posted 27 August 2012 - 10:50 AM
After 6 months the same was vapor inlet temperature: 59 Deg.C and condensate outlet temperature:50 Deg.C utility inlet temperaure: 27 Deg.C and outlet teperature: 29 Deg.C
If i calculate overall heat transfer coefficient for both the cases and shall i consider the performance / efficiency of heat exchnager decreased to ......%.
Edited by dsreenivasareddy123, 27 August 2012 - 10:52 AM.
#5
Posted 27 August 2012 - 12:41 PM
Hope attached documents helps you.
Regards
Shivshankar
Attached Files
#6
Posted 27 August 2012 - 04:37 PM
Compare the fouling design with the actual conditions. The fouling indicates that both have decreased the heat transfer area calculated with respect to design or actual area. You can compare during 15 days the fouling, request that the flow should be the design flow and enter to simulation the temperature, pressure an flow for both sides (cold and hot) once that you validated the design model.
Sometimes is valid to compare UA in normal operating with design but the final decision is compare the heat transfer area.
Edited by Robert Montoya, 11 October 2012 - 10:17 PM.
#7
Posted 28 August 2012 - 06:36 PM
Calculation is one thing but we need basic data like flow rate ( at least on the coolant ) today versus spec sheet , the nature of the material ( any change in the composition) .Any risk to have air pocket which may affect the heat transfer as fouling will do .....
Again more input is needed including a sketch
Breizh
#8
Posted 11 October 2012 - 06:23 AM
Other operational aspect , of course is cleaning of T&S.
A simulation exercise with a simple or an appropriate software will reveal!
And one should see the Delta P as well.
#9
Posted 11 October 2012 - 08:52 AM
That is a big decrease in performance in 6 months. That means the heat load is 1/2 of what it was at the beginning. Is this a new heat exchanger or do you have older performance data? If so does the performance degrade this much each 6 months period?
#10
Posted 29 October 2012 - 09:22 PM
2. The simplest indicative method is by comparing the heat duty based on the cooling medium by assuming the cooling medium flowrate unchanged and specific heat is also unchange. For cooling water for example the ratio of heat duty before anf after is the same as the ratio of temperature difference. Therefore the efficiency in your case:
Eff = (29 - 27)/(31 - 27)*100 = 2/4*100 = 50%
You may use the design temperature difference as your basis for monitoring the ternd of the condenser performance. However, if the cooling water flowrate is not the same as the actual, you need to make necessary adjustment/correction.
Edited by S.AHMAD, 29 October 2012 - 09:29 PM.
#11
Posted 01 November 2012 - 02:37 AM
Please furnish Condensed Methanol Mass Flow Rate in both the cases
SRShah.
#12
Posted 27 December 2012 - 04:51 PM
What is the flow rate / velocity?
I hope the Cooling water is NOT being throttled
I suspect fouling due to cooling water.
If you can provide more information, like geometry, flow rates, cooling water treatment method, you will get a lot more help in trouble shooting from this forum
Similar Topics
Best Heat Exchanger Type For Gas HeatingStarted by Guest_Gole_* , 29 Jan 2024 |
|
|
||
Condenser DesignStarted by Guest_Kentucky08_* , 07 Dec 2025 |
|
|
||
Heat Of Dilution Of Hydrogen Chloride In Hydrochloric Acid Solution (3Started by Guest_fredlan54_* , 21 Nov 2025 |
|
|
||
Water Hammer In CondenserStarted by Guest_Ahmadhamzahperta_* , 31 Oct 2025 |
|
|
||
Shell And Tube Heat Exchanger In HtriStarted by Guest_Sanjayr126_* , 28 Sep 2021 |
|
|

FB