#1
Posted 13 October 2012 - 10:25 AM
May i know why there is no flow meter placed in any flare header in industrial practice ? A flow meter placed in a flare header can alert the DCS personal in case of any valve passing or relief valve passing or any other malfunction? Can anyone help me in this regard?
#2
Posted 13 October 2012 - 11:19 AM
I don’t know where you obtained your information or where your industrial application is located, but here in the USA environmental laws dictate the accountability of ALL gases flared. Depending on the design and operational philosophy of the installation, design may incorporate individual meters on each flare source in order to have operational knowledge and control of any leakage, venting, or process upsets. Or, if regulations permit, one flow meter placed in the main flare entrance. However, bear in mind that such a meter would have to have an approved accuracy over a very wide span of flows – something that may not be available. That is why I am accustomed to seeing individual metering of flare gases. The total gas flared is the sum of the parts.
#3
Posted 14 October 2012 - 02:45 AM
#4
Posted 14 October 2012 - 03:39 AM
This must be a new trend internationally. In local (Greek) refineries regulations are not so strict (yet). I was informed that monitoring of continuous flow emissions (e.g. from stacks) is going to be mandatory in near future (not of intermittent flows, e.g. from PSVs).
Flare header should not contain flow "restrictions" (as once read in API) and some flow meter types can be characterized so. But other types (like ultrasonic flow meters) do not fall in this category.
Attached Files
#5
Posted 14 October 2012 - 05:33 AM
Quite a long time back (5 years back) Ihad raised a query on ultrasonic flowmeters in flare headers and I had got some fantastic responses from the very knowledgable members of "Cheresources". The link is provided below:
http://www.cheresour...are-gas-header/
Regards,
Ankur.
#6
Posted 15 October 2012 - 04:46 AM
For sensing the Safety valve leakage Flow switches again Thermal dispersion type (eseentially Yes Flow/NoFlow sensing) can be installed on sub headers.
Cheers!
#7
Posted 15 October 2012 - 06:13 AM
I have seen separate flow meter provided at inlet of flare system to take invetory of daily flare gas burned.
See attached file for your understanding.
Regards,
Attached Files
Edited by jrtailor09, 15 October 2012 - 06:13 AM.
#8
Posted 15 October 2012 - 09:37 PM
Thanks for all your valuable and useful feedback. Had been really useful
#9
Posted 16 October 2012 - 03:38 AM
#10
Posted 31 January 2013 - 07:25 AM
Could anybody kindly explain the following:
How such flare "knows" that there is a flow in header or there is not when we don't have flowmeter installed?
In other words: I'm interrested how to connect the flare with process. It should burn only in emergency situations. Normaly only pilot burners are ignited. Is ultrasonic flowmeter the only solution?
Similar Topics
Two Phase Reverse Flow -Psv Sizing For Check Valve Failure CaseStarted by Guest_namita.modak1_* , Today, 08:15 AM |
|
|
||
Reverse Flow On Centrifugal CompressorStarted by Guest_Lyne_* , Yesterday, 04:52 AM |
|
|
||
Flow Through A Perforated PlateStarted by Guest_Ahmadhamzahperta_* , 13 Feb 2026 |
|
|
||
Thermal Oxidizer HeaderStarted by Guest_ryn376_* , 29 Jan 2026 |
|
|
||
Gas-Liquid Pipe Flow Friction Loss CorrectionStarted by Guest_Huba_* , 18 Dec 2025 |
|
|

FB