I have attached a spreadsheet to show you what Im doing and the results that i am getting. The numbers in the end do not make sense and I am out of toubleshooting ideas.
Please Help,
Thanks.
|
Posted 10 January 2013 - 12:32 PM
Posted 21 January 2013 - 01:54 PM
Posted 21 January 2013 - 04:17 PM
Posted 21 January 2013 - 04:26 PM
Posted 22 January 2013 - 12:18 AM
Edited by ankur2061, 22 January 2013 - 12:18 AM.
Posted 03 October 2013 - 05:45 PM
Jimmayy, I realize that this discussion is very old but the simple answer to your question is that, as API 521 points out, the Husa formula only applies to purge gas that is lighter than air. Notice that the K values of the components that have molar masses greater than that of air (28.97) are negative. Your resultant weighted average K is negative so the formula does not apply.
Apart from that have you or any one else noticed how small the values are from Husa? Husa did the work for Amoco. Tornado Technologies claims to have a rate from Imperial and Home Oil studies, a rate that is 100 times that of Husa.