Thank you Katmart.
Edited by Pingue2008, 15 March 2013 - 09:47 AM.
|
Posted 15 March 2013 - 09:42 AM
Thank you Katmart.
Edited by Pingue2008, 15 March 2013 - 09:47 AM.
Posted 15 March 2013 - 09:45 AM
Thank you Katmart.
My excel spreadsheet agrees with you all and also with my software
you guys have a great weekend.
Thanks
Posted 19 March 2013 - 03:38 AM
Hi,
1. PFA hysys snapshot. Case 2 and 4 consider no heat transfer is taking place from/to to the pipeline. For upstream pressure 40 barg, ID calculated is 206 mm & velocity 19 m/s (34.5 barg downstream pressure). For upstream pressure 70 barg, ID calculated is 135 mm & velocity 44 m/s (34.5 barg downstream pressure).
2. Please refer to below link where Vmax for natural gas pipeline is discussed.
(Companies like "Shell" recommend that gas velocities in transportation of natural gas through long-distance pipelines should be in the range of 5-10 m/s for continous operation and a maximum up to 20 m/s for intermittent operation) quoted from the same link.
http://www.cheresour...g-calculations/
3. If you need readymade formula for pressure drop calculations, please follow below link.
http://www.cheresour...p-correlations/
Regards.
Ajay
Posted 19 March 2013 - 05:09 AM
Thanks Ajay S. Satpute please i need your help, pls could you send a link to me to be able to install HYSYS v7.3 on my PC, please could you also help me simulate a gas metering station with HYSYS that includes filter seperator, gas scrubber, heater and the pressure regulating and metering facility, i want to know if hydrate will form on the line, i also want to monitor the pressure drop along the line and the gas velocity. Thanks.
Posted 19 March 2013 - 08:08 AM
Hi Funmilayo,
Please ask your company to buy hysys license. As far as I know, it is not available free online. It does have the hydrate formation prediction tool.
Regards.
Ajay
Posted 18 December 2013 - 08:17 AM
You shouldn't attach a new question to the end of an old, existing thread. Rather start a new thread.
Also, be a bit more descriptive. What is 36" and what is 56"? I don't know what you mean giving two diameters.
My old eyes cannot cope with so many zeros all bunched together like that. Either space them out in groups of 3 (eg 750 000 m) or use exponential notation (eg 7.5E5 m).
You should always define what your standard conditions are.
Posted 18 December 2013 - 09:15 AM
36" pipe dimension existing excel spreadsheet .so 56 " pipe diameter can not be calculated.
sorry multi zero.
my question is 56" gas pipe pressure drop for calculation existing excel spreadsheet.
pipe dimeter 56"
wall thickness 26 mm
roughness 10 micron
Inlet Pressure: 90 barg
Outllet Pressure: ? barg
Molecular Weight: 17.04
Tin = 15 deg C
Tsoil = 18.9 deg C
pipe lent :7.5 E5 m
Thank you to everyone
Flow Rate: 100 E6 Sm3 / day
Pipeline Efficiency Factor: 0.95
Density at 15°C, 1 atmosphere 0,72158 kg/std.cu.m
Best regards
Posted 18 December 2013 - 11:43 AM
Fuatender,
please go to the following link and you find an excel spreadsheet that I have put together. just enter the known values and use goal seek to find the missing value (pressure out).
http://www.cheresour...or-natural-gas/
Thank you,
Posted 19 December 2013 - 09:27 AM
Fuatender,
If you have found an error calculating the Reynolds number please share. The spreadsheet has always given satisfactory results and I always check my results with another program before giving to another engineer for back check.So far the spreadsheet has produced good results (Reynolds #, etc...)
Thank you,
Posted 19 December 2013 - 09:35 AM
Thank you for your interest and support . delta p calculation result is correct ,but ı thing reynolds number is not true.
Posted 19 December 2013 - 09:41 AM
Fuatender,
If you have found an error calculating the Reynolds number please share. The spreadsheet has always given satisfactory results and I always check my results with another program before giving to another engineer for back check.So far the spreadsheet has produced good results (Reynolds #, etc...)
Thank you,
ı attach the spreadsheet . 56" pipe results for about reynold number N.G Cals page.
best regards
Edited by fuatender, 19 December 2013 - 10:30 AM.
Posted 20 December 2013 - 11:04 AM
The flow rate you are using is MUCH less than the 100E6 Sm3/day that you specified earlier. It seems that you have converted the length to feet, and then entered that number where the spreadsheet is asking for miles.
Ammonia Line Vapor GenerationStarted by Guest_simadri_* , 07 Apr 2025 |
|
![]() |
||
![]() Flow Through Normally No Flow LineStarted by Guest_iippure_* , 08 Apr 2025 |
|
![]() |
||
Inlet Line Not Free DrainingStarted by Guest_Asifdcet_* , 07 Apr 2025 |
|
![]() |
||
![]() Liquid Liquid Separator SizingStarted by Guest_Kentucky08_* , 03 Apr 2025 |
|
![]() |
||
Alkaline Electrolytic Cell/stack Sizing/design For H2 ProductionStarted by Guest_BRS09_* , 13 Mar 2025 |
|
![]() |