Hi all,
I am doing analysis of existing external floating roof tank, this is API 650 tank with PV vent and emergency vent, i did its sizing for all scenarios which are applicable for such kind of tanks with PV vent and found it adequate to handle loads.
My question is why manufacturer have provided emergency vent for such type of tanks, emergency vent is considered for fire relief cases but for ex floating roof tanks this scenario is unlikely considering fire vapors generated by moderate exposure will be able to escape tank readily and fires of greater magnitude will tip the roof giving the vapor free escape path.
I am less at knowledge of designing of ex floating roof tanks, but i think such tanks roofs are may be of week construction so ex fire scenario is not credible, but what if we are not sure about construction of roof is week or strong???
or if roof construction is strong enough to tolerate pressure resulting from fire, then shall we need emergency vent protection for tanks?
Please have some light over this……
Regards,
Satendra Deshmukh
Edited by satendra, 18 September 2013 - 03:27 AM.