In any steam reformer a properly designed, and tuned, control system should be able to maintain a constant reformer outlet temperature, no matter what the ambient temperature, or its moisture content is.
However when I look at the controls of this unit there seems to be no reformer outlet temperature control. There is TIS2156A/B/C but that seems to be only a 2oo3 voting system for furnace safeguarding (or similar). There is no TIC2156 connected to it to control the fuel firing.
In the fuel control scheme there is no signal coming in from the process to set the fuel fired. The firing only seems to be controlled by PIC2309 and FIC2309. Neither of them gets its setpoint from the reformer outlet temperature. I have the impression that the firing is simply controlled by a manually set duty of 120 Gcal/hr.
Maybe I overlook something, but it seems to me that the firing control of this unit is no more than a duty control, in which the reformer outlet temperature does not play any roll. Moreover the heating value of the PSA tailgas is manual input, and consequently does not change when the composition of the PSA offgas changes.
I have never seen a steam reformer design in which the firing was not controlled by a TIC at the reformer outlet. That TIC can be the master of a duty controller, or of a PIC or FIC on the fuel gas system.
Also I have never seen a steam reformer with an outlet temperature of only 830 oC. I have seen designs ranging from 870 - 930 oC. The lower the outlet temperature, the higher the methane slip.
I wonder, did Haldor Topsoe really design this unit without a TIC to control the reformer outlet temperature?
And did they really recommend to operate this unit at a reformer outlet temperature of only 830 oC ?
Or is this low outlet temperature simply the result of a too low manually set duty at FIC2309 ?
Edited by PingPong, 06 December 2013 - 06:29 AM.