Hello,
I'm currently working to specify a flow regulator to provide steam to an air handler for humidification.
The steam is going to be provided from a boiler at 10-12 psig. Maximum steam requirements to the air handler will be 500 lb/hr, and the boiler is capable of producing over 700 lb/hr steam.
I am working with a very experienced vendor in specifying a flow regulator, and while I trust his recommendation for a regulator, I would like to complete the sizing myself to confirm.
For the Spence K5, 1-1/4" regulator, I have data on Percent Travel vs. CV.
I am looking at two equations from the Spence manual:
- Subcritical flow: W = 2.1*CV*SQRT((P1-P2)*(P1+P2)) , when P2 > 0.58P1
- Critical flow: W = 1.71*CV*P1 , when P2 ≤ 0.58P1
I know my target steam rate (0-500 lb/hr), I know my inlet pressure (10-12 psig), and CV values.
I don't know how to decide my outlet pressure.
The flow regulator will discharge into essentially atmospheric pressure (~0 psig). My instinct is to use the critical pressure equation since my discharge pressure is less than [0.58*10 psig = 5.8 psig] critical pressure, however, this provide critical flow and the theoretical maximum flow out of the regulator. If I use something like 80% of the inlet pressure [0.8*10 psig = 8 psig], I suddenly have an undersized valve even for the 100% open situation.
Could anyone provide any guidance on this?