Hi everyone,
I am going to control the temperature of a highly exothermic reaction via cooling water. The cooling water passes through the tubes located inside the reactor vessel to keep the temperature constant when the reaction is carried out.
I am not sure in such case if it is suitable to control the temperature by a control valve at the upstream of cooling coil or a variable speed pump will be more reliable to control the temperature of the process gas.
Although energy consumption is important, the system is pilot and we are not concerned about the cost of energy and most issue is having the best control on the process temperature.
Following the controlability, the initial cost might be also an important point to compare the VSD pump and control valve.
The cooling pipe size is 1" or 1 1/2" and the flow and head of the cooling pump can be considered around 5 m3/h and 10 mW respectively.
I appreciate your idea if you have some similar experiences.
Mahdi
  • 7,030 posts
Posted 16 April 2019 - 12:27 AM
Hi Mahdi ,
To me the most important is to guarantee the flow of cooling water based on an energy balance .
On a safety point of view do you consider a back up plan in case of power outage , pump failure, agitator broken to prevent run away reaction , do you have all the safety devices in place for pressure built up ?  I'm just worried when people think about pilot plant .
hope this is helping you on your project.
good luck.
#3 thorium90
thorium90
  • 1,073 posts
Posted 16 April 2019 - 02:00 AM
Great point on the safety..
The video below is quite relevant and I think it would be very enlightening as well.
https://www.youtube....h?v=C561PCq5E1g
#4 breizh
  • 7,030 posts
Posted 16 April 2019 - 03:20 AM
hi ,
In addition to my previous answer .
hope this is helping you.
#5 Mahdi1980
Mahdi1980
  • 182 posts
Posted 16 April 2019 - 09:01 AM
Hi Mahdi ,
good luck.
Hi Breizh,
Thanks for your post. Actually, I have considered almost all the safeties such as pressure safety valve, High temperature switch to disconnect the feed to the reactor and a flow switch on the cooling system.
The reactor is fluidized bed, so no agitator is there.
My main focus is already on the suitable control of the temperature.
Mahdi
#6 Bobby Strain
Posted 16 April 2019 - 02:04 PM
May we ask what is the reaction temperature?
#7 Mahdi1980
Mahdi1980
  • 182 posts
Posted 16 April 2019 - 02:20 PM
600 K
#8 Bobby Strain
Posted 16 April 2019 - 04:04 PM
Commercial operations with fluid beds and cooling, like acrlonitrile, make use of steam generating coils. This gives much better temperature control. Control is by varying the steam generation pressure.
#9 breizh
  • 7,030 posts
Posted 16 April 2019 - 09:26 PM
hi,
To add to Bobby's suggestion :
https://www.aiche.or...ep/20141121.pdf
#10 Mahdi1980
Mahdi1980
  • 182 posts
Posted 16 April 2019 - 10:50 PM
hi,
Hi Breizh,
and thanks for the file.
#11 Mahdi1980
Mahdi1980
  • 182 posts
Posted 16 April 2019 - 10:59 PM
Thanks Bobby for your advice. I saw such system in some industrial plant. However, it does not make sense to me.
I mean the control mechanism is unclear for me.
You mean when the cooling water comes through the coil in the reactor, it totally converts to steam?
The water pressure at the inlet of the coil might be at least 3 barg, so to be converted to a 3 bar steam it shall take the heat of reaction to reach 130-140 C water at dew point and take the remaining heat of reaction to convert from saturated water to the saturated steam.
Is it really happen? am I right?
Then how shall I control the temperature by the steam pressure? Can you explain more?
Mahdi
Edited by Mahdi1980, 16 April 2019 - 11:00 PM.
#12 Bobby Strain
Posted 17 April 2019 - 03:14 PM
The cooling tubing is arranged as in a boiler. A separator at the top and a mud drum at the bottom. Risers and downcomers. It operates as a natural thermosyphon with partial vaporization. But you need an experienced professional to help you.