Hi
We have a problem with our diesel backup system for turbine generators and I hope I can get your valuable inputs. I really appreciate for the time you put to go through this long description.
Recently we have found that there are a lot of free water in our diesel system. Strainers were clogged and water samples show diesel bug development in the system. Centrifuges are not also able to remove water effectively. A root cause analysis has been done by the operation team members and the air ingress through the vents into the system and moisture condensation was considered as a main suspect. (An estimate amount of 30 to 50 liter per day of moisture condensation). During the previous 2 weeks we have drained about 20 m3 free water from the system. I tried to red mark the main components of the diesel system contributing to this problem in the attached file.
We have two raw diesel tanks and two treated diesel tanks on south and north part of the platform. The raw diesel tanks are located on the main deck and the treated diesel tanks are located on the higher deck (upper mezzanine deck). The wind direction in our area is from south to north. So, we will have a little higher barometric pressure on the south treated tank and a little lower barometric pressure on the north. We checked the vents on the treated tanks and there is a considerable air breath-in through the vent on south tank and air breath-out through the vents on north treated diesel tank which confirms this pressure differential.This air can communicate with the untreated tanks on the main deck through the overflow lines (red line).
There is also a common header with NO valves (assume that these valves should be always open due to some operational limitations) that is used for periodic filling of raw diesel tanks from supply boats. I should say that the filling lines in the raw diesel tanks have no standpipe inside the tanks. So, the interconnection between these two tanks let the already ingressed air to communicate to both raw diesel tanks and the circulation of air exists between the vapor space of these 4 tanks.
It’s worth mentioning that several years ago, we did some modification on the system. At that time the lift pumps inside the raw diesel tanks were screw pumps with floating suction. But after the modification the screw pumps were replaced with centrifugal pumps (2*100%) without floating suction.
Some alternatives have been already generated to avoid water ingress and condensation and now we are looking for effective and cheapest solution:
1- Installing a manual instrument air blanketing valve instead of normal open vents.
Questions:
a- By manual blanketing, is there still the risk for over-pressurisation of the tank? Do we still need a pressure vent to avoid it?
2- Installing a PVV instead of open vents
Questions:
a- By using a PVV, do we still need to have flame arrestor?
b- How can we manage barometric pressure changes on the PVV?
c- The design pressure for the tanks is 70 mbarg. Is there any procedure or industry practice to determine set pressure and overpressure of the PVV? Should we proceed with set pressure 2.1 mbarg and over-pressure of 4.2 mbarg? How would be the effect of barometric pressure changes on the set pressure?
d- Is there any special operational issue with this solution?
3- Installing standpipe in the filling nozzle of the raw diesel tank and use it as a liquid seal to stop air ingress. This alternative involves difficulties and shutdown requirement for installation.
​Questions:
a- Is hazard of static ignition is valid here (due to splashing of the diesel into the tank without standpipe)? If the answer is yes then we can justify the installation of the standpipe.
And one last question:
Can the centrifugal pump affect the centrifuge performance by making smaller water droplets? (changing the pump is not the main purpose of our evaluation because it is very costly)
Attached Files