what is the minimum volume for crude oil storage tank to install fixed fire fighting system
and if I have standalone crude oil storage tank in desert , is it mandatory to protect it by fixed firefighting system
|
|
Posted 14 June 2022 - 02:16 PM
what is the minimum volume for crude oil storage tank to install fixed fire fighting system
and if I have standalone crude oil storage tank in desert , is it mandatory to protect it by fixed firefighting system
Posted 18 June 2022 - 11:17 PM
Good day,
There may not be a straightforward answer to this. Typically, fire protection requirement is determined based on:
1. Local Regulations
2. Analysis of Fire and Explosion hazard
3. Analysis of local condition (exposure to adjacent properties)
4. Availability of fire department or mutual aid response.
I remembered a discussion in NFPA 30, Chapter 22.8 that for vertical atmospheric fixed roof storage tank (Class-I Fluid) larger than 190 m3 requires a fire extinguishing system if located in a congested area where there is a risk of escalation from on to the storage tank.
So, they are provided if risk warrants the provision and/or the local regulation requires the system to be installed.