Teg Circulation Pump Have Cavitation Issue
26 replies to this topic
#1 rizwangoheer
rizwangoheer
  • 30 posts
Posted 04 July 2022 - 07:53 AM
Good day All,
I need your advise regarding the cavitation issue in Lean TEG Circulation pumps in Gas Dehydration unit. In our Gas Plant, there are 3 Gas Dehydration units and all have the same problem with pump cavitation. Each unit is provided with dedicated TEG Contactor, Stripper and TEG Circulation with all other required equipment for TEG unit.
These are old units running normal since last 10 years but now having this problem.
we tried the following to find the root cause of the cavitation issue but still no success:
1- Lean TEG analysis shows 99.9% TEG with remain water content
2- Pump suction strainer is clean
3- Suction operating condition are same as normal
4-Foaming tendency test shows no foaming
5- No air ingress as there is no leakage in suction line
6- all suction and discharge valves are opening as per lineup
Please advise if there is any this we should do to find the root cause of this issue.
reagrds,
Edited by rizwangoheer, 06 July 2022 - 11:13 AM.
  • 6,791 posts
Posted 04 July 2022 - 08:13 AM
Can you share a PID of the corresponding column  with pump and detail of the suction line?
#3 Pilesar
  • 1,567 posts
Posted 04 July 2022 - 09:57 AM
If these pumps are supplied from the same column bottom nozzle, I suspect some of the column internals have moved from where they are supposed to be and are partially blocking the pump suction path. Check the line pressure near the pump suction to see if the pressure drop in the suction line is excessive.
#4 Bobby Strain
Posted 04 July 2022 - 11:18 AM
Your query is ambiguous: "there are 3 units".
#5 rizwangoheer
rizwangoheer
  • 30 posts
Posted 04 July 2022 - 11:38 PM
 we open the suction strainer of pump but its clean with no materail which can block the suction
#6 rizwangoheer
rizwangoheer
  • 30 posts
Posted 04 July 2022 - 11:40 PM
 Sorry if this is not clear. Actually there are 3 Gas Dehydration units and each one is provided with dedicated TEG Contactor, Stripper and TEG Circulation Pump. Actully feed wet gas is distributted in all three units for dehydration. Hope its clear now.
#7 rizwangoheer
rizwangoheer
  • 30 posts
Posted 04 July 2022 - 11:41 PM
I tried to attach P&IDs but no luck. I will try again.
#8 breizh
  • 6,791 posts
Posted 04 July 2022 - 11:52 PM
Go to edit and use full editor to upload your PID,
Now regarding suction line , it's not because the strainer is clean that the suction is not partially obstructed . You need to check the line starting at the bottom of the column .
#9 latexman
  • 1,838 posts
Posted 05 July 2022 - 06:52 AM
These are old units running normal since last 10 years, but now having this problem.
Sounds like it's time to open the column for inspection.
#10 Bobby Strain
Posted 05 July 2022 - 09:28 AM
Are the pumps centrifugal? A photo showing the stripper bottom and piping to the pump, including the pump, might be helpful. And you should review incidents when the cavitation began. Since all three units are effected, the cause is likely to be associated with the feed gas. I presume the feed comes from a common separator. So it's likely that an upset carried liquid with the gas. And it contained some contaminate that deposited somewhere in the pump suction from the stripper.
Edited by Bobby Strain, 05 July 2022 - 11:16 AM.
#11 rizwangoheer
rizwangoheer
  • 30 posts
Posted 05 July 2022 - 11:40 PM
We have 3 separate Dehydration units and TEG circulation pump in all 3 units is showing the same problem. Can all three column have problem at the same time.
#12 rizwangoheer
rizwangoheer
  • 30 posts
Posted 05 July 2022 - 11:44 PM
Please  see attached pump pfd and pid.
Yes these are Centrifugal pumps and this cavitation phenomena happened multiple times in a day. Cavitation happen for 3-4 minutes with changes in pump sound and low discharge pressure.  After few minutes it become normal.
We are investigating the feed gas changes if any which can cause this kind of upset in TEG circulation pump.
regards,
Edited by rizwangoheer, 06 July 2022 - 11:18 AM.
#13 latexman
  • 1,838 posts
Posted 06 July 2022 - 06:14 AM
That's less likely, unless it's a common cause.
Yes these are Centrifugal pumps and this cavitation phenonema happeded multiple times in a day. Cavitation happen for 3-4 mintues with chnages in pump sound and low discharge pressure.  After few mintues it become normal.
We are investigating the feed gas chnages if any which can cause this kind of upset in TEG circulation pump.
During this 3-4 minute event, have/can you grab a sample and analyze?
#14 rizwangoheer
rizwangoheer
  • 30 posts
Posted 06 July 2022 - 11:15 AM
please see attached pump pid and pfd
#15 latexman
  • 1,838 posts
Posted 06 July 2022 - 11:50 AM
Sorry, no attachments.  If you edit your post and then click on "Use Full Editor", go to the area under the text box to attach the files.  If you have issues, try to describe in detail what is happening, so we can help.
#16 rizwangoheer
rizwangoheer
  • 30 posts
Posted 06 July 2022 - 11:00 PM
There is an attachment in my updated post. Please see below screenshot.
#17 rizwangoheer
rizwangoheer
  • 30 posts
Posted 07 July 2022 - 02:16 AM
Good day All experts here.
Please help to provide some advise on problem i mentioned in my post. i also attcahed the requested P&IDs and PFDs for the pump.
regards,
#18 breizh
  • 6,791 posts
Posted 07 July 2022 - 03:56 AM
Consider to read the documents attached to support your work.
Do you have a way to monitor the Pressure and temperature at the suction of the 3 pumps ?
Did you investigate the possibility of gas carry over ? light component !  What about emulsion / foam which could cause a change in the density of the liquid .
Talking about cavitation , did you notice some damage on the impellers of the pumps ( erosion, holes ..)?
#19 latexman
  • 1,838 posts
Posted 07 July 2022 - 06:07 AM
Ah ha!  You put it in the original post (OP).
#20 rizwangoheer
rizwangoheer
  • 30 posts
Posted 07 July 2022 - 06:36 AM
Yes we have pressure and temperature monitoring at pump suction but shows normal conditions no change. Regarding gas carry over, we are working with plant operation team to investigate if this is the case. We also checked the foaming and emulsion issue but its not.
Regarding pump impeller damage, we did not open the pump yet as this problem satrted few days back. we will do this if issue not resolved.
#21 rizwangoheer
rizwangoheer
  • 30 posts
Posted 07 July 2022 - 06:37 AM
Sorry for the inconvenience. You want to suggest something which we can check to find the root cause of the issue.
#22 latexman
  • 1,838 posts
Posted 07 July 2022 - 06:45 AM
 No problem.  I'm waiting on a reply to my last suggestion (Post 13).
#23 Pronab
Pronab
  • 166 posts
Posted 15 July 2022 - 01:03 AM
Usually TEG circulation pump is reciprocating. I don't see any heat recovery/temperature drop of lean TEG before entering to TEG pump suction. (TEG pressure/Temp as your material balace: 6.5 psig & 359 Deg F(181 Deg C). Normally there is a Plate Heat Exchanger (PHE) before TEG entering to pump suction and a HH Temperature trip of TEG Circulation pump to avoid TEG degradiation (usually TEG bath temperature is maintain at 204 Deg C and not to exceed 210 Dg C). In your attachment there is no such PHE or Temp HH to trip of pump. We have two dehydration unit where TEG circulation pump operating temperature is 80 Deg C and a HH temperature is 130 DegC. I surprised to see your TEG Circulation pump temp is 181C (as lean TEG temp). As you mentioned plant were running 10 years before smooth and now creating problem. Is there any change/modification of the plant? Compare the data before and after 10 years. I am afraid TEG reach to vapor state whenevr it enter into pump suction and a result of cavitation.
Edited by Pronab, 15 July 2022 - 01:04 AM.
#24 horatorres
horatorres
  • 88 posts
Posted 18 July 2022 - 08:28 PM
  There is a commun fact, check
1. Plug in the suction line. No only the filter
2- Check the vortex, something coming in the feed creates a gum in the vortex increasing the pressure drop till cavitation.
3. Check the TEG, a light component could reduced your Vapour pressure-
Horacio
#25 Pronab
Pronab
  • 166 posts
Posted 24 July 2022 - 02:29 AM
Dear Mr. rizwangoheer
Could you please share whether your TEG pump problem solved?