Check Valve Location
#1
Posted 26 May 2023 - 04:57 PM
#2
Posted 26 May 2023 - 10:32 PM
So the actuated valve is to be open all the time unless there is high high pressure detected? Then the location of the actuated valve will not affect normal operation and I don't think it really matters as long as you can block in the check valve for maintenance. I would probably choose to put the actuated valve closest to the source of the high high pressure unless there is reason for the other location.
#3
Posted 26 May 2023 - 11:07 PM
#4
Posted 27 May 2023 - 01:15 AM
Hi,
Tell us what your reasoning is, someone will acknowledge or not!
Behave like an engineer, do not only bring open questions.
This is the way it works.
Note: The actuated valve should be close to the source.
Good luck
Breizh
#5
Posted 27 May 2023 - 07:09 AM
Edited by sn_sn, 27 May 2023 - 07:32 AM.
#6
Posted 27 May 2023 - 07:36 AM
Hi,
I did not intend to insult you, my bad.
My point is the following, whenever possible describe the scenario with supportive documents, explain your proposal and ask for confirmation.
Good luck in your engineering career.
Breizh
#7
Posted 27 May 2023 - 09:47 AM
With the PT, ABV and high pressure shutdown, do you still need the CK valve? I realize CK valve is cheap backflow protection, and it may be easier now to leave it than remove it. Maybe you need both for PHA or something.
Also, is the source of high pressure scenarios upstream of the PT, downstream of the PT, or both? Just be careful when the ABV closes, it does not blind the PT of the pressure source(s).
#8
Posted 30 May 2023 - 03:11 AM
It seems that you are designing one back flow protection with actuated valve (interlock with HH differential pressure) as well as check valve.
Actually, the loop (HH dp + logic + actuated valve) provide the credit for protection. And the check valve is not an independent protection layer. So there is no different for its location. It also can not change the pressure break point, so all the pipeline should be the same class.
But if you consider maintenance the check valve, you should select one point which isolation is easy to be done.
This is not something confidential, it is just common engineering practice.
#9
Posted 07 June 2023 - 09:42 AM
Generally, I'd prefer to put the boundaries of any unit operation isolated by manual valves. thus any actuated devices to be inside this boundary. this is just a common practice in my career.
thanks
Similar Topics
Check Valve FailureStarted by Guest_Falah_* , 26 Mar 2025 |
|
![]() |
||
Multiport Selector Valve (Msv)Started by Guest__1angelia23_* , 12 Mar 2025 |
|
![]() |
||
![]() Valve Cavity - Pressure Relief ValveStarted by Guest_CS10_* , 20 Feb 2025 |
|
![]() |
||
![]() Strategy For Adequacy Check Of Multiple Bdvs In A SystemStarted by Guest_nabeelsp1036_* , 22 Jan 2025 |
|
![]() |
||
![]() Valve Cv InputsStarted by Guest_QuantumEng_* , 01 Apr 2024 |
|
![]() |