I have 2 PSV's close to each other. Both PSV discharge to atmosphere and each have vent silencer. Is it possible to use 1 commn silencer for both PSV discharges? I have a simple sketch attached.
|
Posted 25 July 2023 - 05:53 AM
I have 2 PSV's close to each other. Both PSV discharge to atmosphere and each have vent silencer. Is it possible to use 1 commn silencer for both PSV discharges? I have a simple sketch attached.
Posted 25 July 2023 - 08:01 PM
Hi,
What is the problem with the existing setup?
To me, NO, you have a risk to affect the operation.
Breizh
Posted 26 July 2023 - 01:33 AM
Hi,
What is the problem with the existing setup?
To me, NO, you have a risk to affect the operation.
Breizh
Thanks Breizh. Actually, the system is not existing. I wonder if its possible to connect 2 PSVs outlets to 1 common silencer. Is there any point that I have to pay attention?
Posted 26 July 2023 - 01:35 AM
I have 2 PSV's close to each other. Both PSV discharge to atmosphere and each have vent silencer. Is it possible to use 1 commn silencer for both PSV discharges? I have a simple sketch attached.
Hi,
In general and concerning back pressure standpoint, if two PSVs won't pop up simultaneously appears there would be no problem having common silencer for such two PSVs discharges...
Posted 26 July 2023 - 01:48 AM
HI,
You may want to contact these guys to get a definitive answer:
https://www.valvulas...lencers_eng.pdf
I believe a silencer is designed for a specific flowrate (design).
Breizh
Posted 26 July 2023 - 05:55 AM
Common header/vent is a normal practice if sound engineering has been applied.
Pay attention that in your case superimposed backpressure is variable and depends on built-up backpressure during relief. Balanced design of both PSV is preferred.
Means should be applied to avoid a relief fluid from opened PSV gets to outlet lateral pipe of closed PSV.
![]() Multiple Tanks Venting To Common ScrubberStarted by Guest_Rudra_* , 02 Feb 2021 |
|
![]() |
||
Hipps Sil-3 During Vs Flare Loading During Common Failure ScenarioStarted by Guest_Beergson_* , 15 Jan 2021 |
|
![]() |
||
Actace Band Sound Pressure From SilencerStarted by Guest_shvet1_* , 21 May 2020 |
|
![]() |
||
Controlling Pressure On Common HeaderStarted by Guest_RobertJAnderson91_* , 03 Oct 2019 |
|
|
||
Pumps Operating Under A Common Suction Header But With A Segregated DiStarted by Guest_SawsanAli311_* , 02 Sep 2018 |
|
![]() |