Firewater Demand
#1 saiedeh
saiedeh
  • 12 posts
Posted 16 October 2023 - 02:00 AM
I have a problem for calculating the firewater demand in fire scenario in a plant. There are columns, vessels, heat exchangers, reboilers and aircoolers in the plant. Which equipment shall be taken into account for calculating the firewater.
Please note that in NFPA 15, only mentioned that vessel areas should be considered. What about other types of pressure vessels, like reboilers, exchangers, etc.?
Thank you for your help.
#2 Zauberberg
Zauberberg
  • 2,728 posts
Posted 21 October 2023 - 02:52 PM
If you are focused on prescriptive methods, refer to API 2001.
If you want to look at real life scenarios (i.e. considering actual configuration / volumes of your plant and equipment and what could go wrong), organize a team consisting of Process Engineer, Tech Safety, Operations, and identify realistic fire scenarios - consider how far they could possibly escalate. Then, design the fire protection system capable to cope with these events.
#3 breizh
  • 7,039 posts
Posted 21 October 2023 - 10:24 PM
You may want to take a look at the documents attached.
#4 Biomass Process
Biomass Process
  • 14 posts
Posted 17 August 2024 - 12:24 PM
Can you please the documents as it is not attached .
#5 breizh
  • 7,039 posts
Posted 17 August 2024 - 10:18 PM
hi, I will in a couple of days.
#6 breizh
  • 7,039 posts
Posted 19 August 2024 - 07:50 AM
Consider the documents attached.
Past projects in China and Thailand, requirements were 2000 m3 and 1300 m3 capacity, for 2 hours operation.
For China a spent water pond for 2000 m3.
Note:
You should consult also your safety bureau and /or the fire brigade and/or the Insurance Broker in charge of the facility where the project is being installed.
#7 Biomass Process
Biomass Process
  • 14 posts
Posted 01 October 2024 - 12:29 PM
Thank you very much