Hello Guys.
I attached a picture summarizing the process. I receive the project on the basic engineering stage and i'm doing the detail engineering over it. My problem is that I believe this system is overdesigned with too much relief valves.
It is an water electrolisys hydrogen production facility. I have three parallel electrolizers production hydrogen at 0.3 barg and around 1.000 kg/h total. The equipment has a relief valve that will open in case of high pressure inside the electrolizer package.
At the compressor suction, I have another pressure control system that I believe is redudant. The only reason there is to install a high pressure relief valve on the suction of the compressor in the case that that the compressor's bypass valve fails open.
Downstream the compressor there is another relief valve. I believe this one is well positioned since if something downstrem the compressor fails, or a valve is closed, I'll need to relieve the excess product. The pressure discharge of the compressor is set at 35 barg.
My main concern is on the third and forth relief valves, the one after the purification and the one before mixing hydrogen with nitrogen. The basic engineer developer probably tought he should put a relief valve downstream every automatic block valve. I know this because I've receive two versions of the syngas mixing station and from one version to the other the designer added both the on-off valve and the relief valve.
The compressor and purification units are really close together (less than 30 m apart), but the mixing is done in a different site around 1000 meters away.
Downstream the syngas mixing there is another pressure control valve, but that one has a different set point and it's purpose is to regulate the pressure one the reformer (out of scope of this project).
I would like your experinced opinion on this arrangement (pressure relief before automatic block valve). Is there a reason to keep all of them? Does it add some degree of safety on the process, or are them more points of failure? Could all the flow be relieved from the valve on compressor outlet?
Thank you all,