Prv Fire Case Load Calculation For Mixture.
#1
Posted 24 June 2024 - 11:55 AM
#2
Posted 25 June 2024 - 12:40 AM
you can adopt some "conservative" estimate (see API etc.) or try to solve phase equilibria + heat balance, several tools available, see for example this previous thread :
https://www.cheresou...ure-using-hysys
#3
Posted 25 June 2024 - 12:20 PM
You may find useful discussion from several years ago: https://www.cheresou...f-vaporization/
#4
Posted 29 June 2024 - 01:48 AM
Please share your engineering practice or opinion on this case.
For such cases we use equilibrium vapor composition at relieving pressure
#5
Posted 29 June 2024 - 05:41 AM Best Answer
Please share your engineering practice or opinion on this case.
We use the component with the lowest heat of vaporization. It is simple and conservative.
#6
Posted 08 July 2024 - 12:36 PM
Dear All,
Sorry for the late response and thanks for every comments.
I solved this problem with using the component with the lowest heat of vaporization.
Even assuming relieving component as TEG, it didn't cause any major concerns.