#1
Posted 05 September 2024 - 01:14 PM
I'm seeking clarification on whether hydraulic resistance from piping and components (e.g., heat exchanger pressure drop) should be considered as a credit when calculating PSV relief rate for an upstream control valve failing wide open.
My system:
- Battery Limit Pressure: 18 Barg
- Control Valve: Reduces pressure to 1.5 barg
- Line: 10 ft
- Heat exchanger: specific pressure drop
- Packed bed: specific pressure drop
- Manual valves: ~80% open
- Blower (design pressure: 3 barg): PSV location
Should the relief rate account for all component resistances as flow increases, or should it be sized based on 18-3x1.1 pressure differential?
#2
Posted 05 September 2024 - 02:41 PM
#3
Posted 05 September 2024 - 04:35 PM
Hello,
I'm seeking clarification on whether hydraulic resistance from piping and components (e.g., heat exchanger pressure drop) should be considered as a credit when calculating PSV relief rate for an upstream control valve failing wide open.
My system:
- Battery Limit Pressure: 18 Barg
- Control Valve: Reduces pressure to 1.5 barg
- Line: 10 ft
- Heat exchanger: specific pressure drop
- Packed bed: specific pressure drop
- Manual valves: ~80% open
- Blower (design pressure: 3 barg): PSV location
Should the relief rate account for all component resistances as flow increases, or should it be sized based on 18-3x1.1 pressure differential?
Hi,
Yes, in general all components resistance would affect the PSV relief rate...
#4
Posted 05 September 2024 - 10:49 PM
Hi,
The answer is Yes, all pressure losses should be considered.
Consider this handbook to support your work.
Breizh
Attached Files
#5
Posted 06 September 2024 - 03:29 AM
Yes, one can take credit of the losses in the fittings and equipment.
My two cents:
1) If you are calculating for brownfield project, go ahead and consider these loss
2) If you are calculating for green field, do not consider these losses and do conservative calculations, because a lot of thing change and you might end up in re-doing the calculation at a later date.
Similar Topics
Answered
Ahu Chilled Water Hot Water Control And FunctioningStarted by Guest_RAMSAI_* , 23 Sep 2024 |
|
|
||
Closed Loop Pump Suction Line Sizing CriteriaStarted by Guest_Afshin445_* , 30 Aug 2024 |
|
|
||
Barometric Legs Line SizingStarted by Guest_panagiotis_* , 17 Mar 2023 |
|
|
||
Ways To Reduce Wetted Surface Area In Psv SizingStarted by Guest_KoreaGyu_* , 21 Aug 2024 |
|
|
||
Process Gas Compressor - Capacity Control ValveStarted by Guest_CHSO4_* , 18 Jul 2024 |
|
|