3
Screening Heat & Material Balances Cases For Fire Relief Psv Sizin
#1 powerox6
powerox6
  • 9 posts
Posted 21 August 2026 - 07:39 AM
Hello Professionals,
I am sizing a PSV attached to a TEG filter, where the selected overpressure scenario is Fire Case. There are several heat and material balance (HMB) cases, which have varying operating conditions and fluid properties. Just for the sake of comparing I have run all cases with the reference stream taken at the inlet of my vessel. The results are as follows. My question is, how would I know how to screen for the HMB cases in order to get the maximum relief load and/or orifice area? By the trend in the table below, it seems that the maximum relief occurs with the case which has the highest overall MW and highest liquid fraction. Is this always the case? Are there any other fluid properties which I must look for in order to determine the governing HMB case?
Edited by powerox6, 21 August 2026 - 07:43 AM.
#2 latexman
  • 1,928 posts
Posted 21 August 2026 - 09:06 PM
Maximum relief load is relevant, but maximum orifice area is what you are really after!
#3 powerox6
powerox6
  • 9 posts
Posted 22 August 2026 - 02:10 AM
Yes. I've had cases where the relief load for a particular case is higher, but the maximum orifice area is in another case with lower relief rate.
#4 carlos infante
carlos infante
  • 32 posts
Posted 23 August 2026 - 02:20 AM   Best Answer
Power
You must choose the case with the higher orifice area for the PRV. API 521 defines it as the worst-case scenario.
Carlos
#5 powerox6
powerox6
  • 9 posts
Posted 23 August 2026 - 08:08 PM
Thanks Latex & Carlos
#6 breizh
  • 7,051 posts
Posted 23 August 2026 - 10:12 PM
Consider reading these documents.
#7 powerox6
powerox6
  • 9 posts
Posted 24 August 2026 - 05:02 AM
Thanks Breizh