This is about the pressure drop specification for a plate heat exchanger application required in our process. Would allowable pressure drop of 0.5 bar be appropriate or should it be 0.8 bar?
In Plate Heat Exchanger application as a user, what is the optimal pressure drop specification for a case with almost equal flow of good quality water on both sides and temperature change (only sensible heat transfer) on both sides. Relatively, there seems to be a substantial pressure drop used up in the inlet and outlet nozzles, besides the pressure drop effectively used through the channels used in actual heat transfer. The flow conditions are as follows --
Hot water / Cold water
Water flow, kg/s 600 600
Temperature In, deg. C 130 120
Temperature Out, deg. C 125 125
Fouling factor may be considered as practically zero.
Thank you for your comments.
|
|
Optimal Pressure Drop - Plate Heat Exchanger
Started by Sadananda Konchady, Jan 04 2007 01:35 AM
2 replies to this topic
Share this topic:
#1
Posted 04 January 2007 - 01:35 AM
#2
Posted 05 January 2007 - 06:17 AM
Normally PHE's pressure drops are determined by the flow through plate channels.
Within the plate, the friction factors are in general much higher than those inside a tube for the same Reynolds number. However, nominal velocities are low and plate lengths limited, so that the term v2L/2g in the pressure drop equation is much smaller than those normally encountered in tubulars.
The friction factor is correlated with:
ΔP =f ρ v2L/2g ; f = B/Rey
where y varies from 0.1 to 0.4 in turbulence and B is a constant characteristic of the plate.
In the specific, your PHE looks pretty big (duty ca. 12MW) ... I estimated 0.9 bar pressure drops (0.2 through ports + 0.7 through channels) so I suggest to verify if your system can allow for at least 1 bar pressure drops.
Hope this can help.
_Lf
Within the plate, the friction factors are in general much higher than those inside a tube for the same Reynolds number. However, nominal velocities are low and plate lengths limited, so that the term v2L/2g in the pressure drop equation is much smaller than those normally encountered in tubulars.
The friction factor is correlated with:
ΔP =f ρ v2L/2g ; f = B/Rey
where y varies from 0.1 to 0.4 in turbulence and B is a constant characteristic of the plate.
In the specific, your PHE looks pretty big (duty ca. 12MW) ... I estimated 0.9 bar pressure drops (0.2 through ports + 0.7 through channels) so I suggest to verify if your system can allow for at least 1 bar pressure drops.
Hope this can help.
_Lf
#3
Posted 11 January 2007 - 05:59 AM
Thanks, Palusa for the suggestion to increase the permissible pressure drop to 1 bar. There must be an optimum from the customer's view point since the pumping power required would also increase as the permissible pressure drop is increased.
I will check this further when floating enquiries to PHE vendors.
Regards,,
Escape
I will check this further when floating enquiries to PHE vendors.
Regards,,
Escape
QUOTE (palusa @ Jan 5 2007, 06:17 AM) <{POST_SNAPBACK}>
Normally PHE's pressure drops are determined by the flow through plate channels.
Within the plate, the friction factors are in general much higher than those inside a tube for the same Reynolds number. However, nominal velocities are low and plate lengths limited, so that the term v2L/2g in the pressure drop equation is much smaller than those normally encountered in tubulars.
The friction factor is correlated with:
ΔP =f ρ v2L/2g ; f = B/Rey
where y varies from 0.1 to 0.4 in turbulence and B is a constant characteristic of the plate.
In the specific, your PHE looks pretty big (duty ca. 12MW) ... I estimated 0.9 bar pressure drops (0.2 through ports + 0.7 through channels) so I suggest to verify if your system can allow for at least 1 bar pressure drops.
Hope this can help.
_Lf
Within the plate, the friction factors are in general much higher than those inside a tube for the same Reynolds number. However, nominal velocities are low and plate lengths limited, so that the term v2L/2g in the pressure drop equation is much smaller than those normally encountered in tubulars.
The friction factor is correlated with:
ΔP =f ρ v2L/2g ; f = B/Rey
where y varies from 0.1 to 0.4 in turbulence and B is a constant characteristic of the plate.
In the specific, your PHE looks pretty big (duty ca. 12MW) ... I estimated 0.9 bar pressure drops (0.2 through ports + 0.7 through channels) so I suggest to verify if your system can allow for at least 1 bar pressure drops.
Hope this can help.
_Lf
Similar Topics
Pressure BuildupStarted by Guest_Yankee_* , Yesterday, 05:31 AM |
|
|
||
Spray Dryer Nozzle Issue – Pressure Increase And Fines IncreaseStarted by Guest_Ella2365_* , 24 Mar 2026 |
|
|
||
The Basis Of Calculation To 3% Pressure Loss At The Inlet Of PressureStarted by Guest_phoenixmoca_* , 14 Mar 2026 |
|
|
||
Mdmt Basis For Gas Let-Down From High-Pressure Storage (Non-Blowdown CStarted by Guest_naghizad_* , 27 Feb 2026 |
|
|
||
Selection Of Heat Exchanger For Heating LiquidStarted by Guest_fahctory_* , 24 Feb 2026 |
|
|

FB